I have a 240 volt 50 amp electric kiln with a 3 prong plug. I have a 4 prong outlet for a dryer I would like to use. The kiln has 2 hots and the ground hooked up. Can I hook the new 4 prong cord up and just leave the neutral disconnected? Of course I don't want to burn down the house and wanted an expert opinion


Thanks!
 

·
Super Moderator
Joined
·
8,866 Posts
The rating on the dryer receptacle is 30 amps, and the kiln is rated for 50.
You can not use the dryer receptacle.
 

·
Registered
Joined
·
9 Posts
Discussion Starter #3
I am a little confused about that because on one place on the kiln it says 50 amps and another place it says 25 amps
 

·
Electromagician
Joined
·
79 Posts
I am a little confused about that because on one place on the kiln it says 50 amps and another place it says 25 amps
sorry but that is electrical hieroglyphics' for man the lifeboats we are way over our heads here. :laughing:
 

·
Semi-Pro Electro-Geek
Joined
·
3,403 Posts
I am a little confused about that because on one place on the kiln it says 50 amps and another place it says 25 amps
Well you better figure that out for sure! Look on the rating plate of the kiln where it lists voltage, current, and probably wattage.
 

·
Registered
Joined
·
9 Posts
Discussion Starter #6
See below. At the top it says 25 amps, but down below it says 50 amps. Its a cress model 328J kiln but I couldn't find much online.

 

·
Registered
Joined
·
9 Posts
Discussion Starter #8
So I emailed Cress and they said, "Go with the top decal, 25 amps." Also the real model number is B23H which is closest to this one
 

·
Registered
Joined
·
9 Posts
Discussion Starter #10
So back to my question. The kiln has 2 hots and the ground hooked up. Can I hook the new 4 prong cord up and just leave the neutral disconnected?


Thanks!
 

·
Semi-Pro Electro-Geek
Joined
·
3,403 Posts
See below. At the top it says 25 amps, but down below it says 50 amps. Its a cress model 328J kiln but I couldn't find much online.
It requires 25A. The lower label is on the Kiln Sitter, which is a completely separate device made by a separate company and installed as part of the kiln. The Kiln Sitter is a timer and automatic shutoff (using pyrometric bars) for the kiln, and the 50A rating is it's maximum allowable load. The upper nameplate is for the kiln itself, and says 25A.

Use a 4-wire cord and leave the neutral (white) disconnected.
 

·
Registered
Joined
·
9 Posts
Discussion Starter #13
The hots on the old cord are both white. Does it matter which one goes where (red and black)? I will connect green (ground) and leave white disconnected.
 

·
Semi-Pro Electro-Geek
Joined
·
3,403 Posts
The hots are interchangeable. Just make sure the ground goes to the frame.
 