Hello All,
First Time Poster- I am so glad I found this forum today. I've read through several threads and there seems to be tons of great info, but I wanted to get a little bit specific on my issue and see what some of you think. I am a mechanical engineer so I have some electrical background (changed switches/outlets etc and understand basic wiring), but I'm not too comfortable messing with the panel yet etc.
Here is the kinda brief version, and then if you want the details, you can read the rest:
My water pipe main in (from the street to my basement), has had pinhole leaks 6 times in the 2.5 years since I've moved into my townhouse. 20 year old construction, no one else in the 200 units has had this happen once to their pipes. Water company thought it could be electrical related, so we tested last year and there was stray current in the earth.
I've borrowed a clamp meter and there is current that is on my water pipe (right where it exits the basement). When the furnace (forced hot air) kicks on, I get about a 1.2A spike on the pipe. When I plug in an appliance and it's pulling a load, the current is directly additive on the waterpipe. I thought it was a specific outlet, but I plugged a vacuum in about 10 different outlets in the house, and every time I see a spike of about 1.5A on the water pipe when it turns on.
The ground wire that is clamped to the water pipe was loose, and has been since tightened, but still the current goes all on the water pipe and none on the ground wire.
I've had an electrician check my panel and he said everything looked good there. Tightened everything up etc. We thought it was a neutral touching a ground wire somewhere in an outlet, but when it happens for every outlet, we thought it would be a faulty neutral return (from my panel to the transformer across the street. Wiring is underground. Had Con Edison (my electric provider) check it out and I replicated the issue for them, they did some tests and had said it was a faulty neutral so they put a shunt up while they waited to do permanent repairs (said they were going to dig and fix). Now, they tell me it's fixed, but they did no digging.
Current still exists on the water pipe when either the furnace goes on, or when I plug in anything.
a) What is going on?! How do I fix this??
b) If the ground is constantly taking current, does that make sense that it could act as a catalyst to cause the copper pipes to corrode, and thus keep getting pinhole breaks? FYI I had 3 in December this year, and that kind of kicked this into high gear. I had thought that A/C current shouldn't cause corrosion- only DC. Or is it possible that voltage is arcing to the pipe and causing a sudden pinhole break?
//////////////
Some more details:
We know the water pipe gets a leak when I hear a hissing noise in the basement. I currently have a leak but the town is waiting to dig it up until I get this electrical issue fixed. They want to install a dielectric union on the water pipe between their main and my pipe. This makes me nervous because Con Edison told me our zone is coded so that the water pipe is the primary ground. So they would break this path, and thus where would my ground go? The electrician said he could put in 2 more ground rods to make sure that I have a strong ground in place if they do this. I think this is a good idea, but is more a safety backup rather than fixing the problem.
The leaks always seem to show up when it gets cold out, but I don't think they are caused by freezing (since they are 4ft underground). My thoughts are that the furnace circuit is somehow bad and once that starts turning on, it accelerates the process, or starts creating that constant current on the water pipe, and maybe this stresses it till it pops.
I have replaced switches/outlets in the townhouse, as well as a few light fixtures, but I'm pretty positive I know what I'm doing and wired everything correctly. Pretty much one at a time, and just copy the previous wiring. I also do not think I caused this because i found out it happened before I moved in. Also all the lights/switches work, and I used a polarity tester and never showed anything flipped etc. Also there never is any dim/flickering lights or weird situations where the power seems not to be full.
I tried to isolate the circuit by testing different combinations on the breaker. That is how I found out the when the heat goes on, the current always spikes. I also so that when the drier was on, I get a spike, which then led me to test many appliances. Pretty much when anything goes on or is plugged in, and is pulling a load, that amperage shows up on the water pipe.
I've spoken to some EEs at work who I consider very smart. They say most likely that somewhere the neutral is bleeding to ground.
How can I tell if this is Con Edisons responsibility (bad neutral on their side), or if it is on my side somewhere.
Hypothetically if a light fixture wire nut wasn't tight and the neutral was touching the ground somewhere, could that be the cause of this? I thought only that circuit would show the effects of the current bleed onto the ground, or are all the neutrals tied together before the panel somewhere? I'm trying to figure out how every one of my outlets in the house causes current to go on the ground. There is no way they all are wired incorrectly.
I know it's long winded, but this has been quite a stumper. The electrician thought it was a bad neutral on Con Edison's side, but I don't know if he was being lazy and didn't check something on my side. I am capable of checking every switch/outlet in the house to find the problem, but I'd love to avoid that if I don't have to as it will be time consuming and annoying with some fixtures.
Thanks a ton in advance, and looking forward to any help/insight you can share.
-Dan
First Time Poster- I am so glad I found this forum today. I've read through several threads and there seems to be tons of great info, but I wanted to get a little bit specific on my issue and see what some of you think. I am a mechanical engineer so I have some electrical background (changed switches/outlets etc and understand basic wiring), but I'm not too comfortable messing with the panel yet etc.
Here is the kinda brief version, and then if you want the details, you can read the rest:
My water pipe main in (from the street to my basement), has had pinhole leaks 6 times in the 2.5 years since I've moved into my townhouse. 20 year old construction, no one else in the 200 units has had this happen once to their pipes. Water company thought it could be electrical related, so we tested last year and there was stray current in the earth.
I've borrowed a clamp meter and there is current that is on my water pipe (right where it exits the basement). When the furnace (forced hot air) kicks on, I get about a 1.2A spike on the pipe. When I plug in an appliance and it's pulling a load, the current is directly additive on the waterpipe. I thought it was a specific outlet, but I plugged a vacuum in about 10 different outlets in the house, and every time I see a spike of about 1.5A on the water pipe when it turns on.
The ground wire that is clamped to the water pipe was loose, and has been since tightened, but still the current goes all on the water pipe and none on the ground wire.
I've had an electrician check my panel and he said everything looked good there. Tightened everything up etc. We thought it was a neutral touching a ground wire somewhere in an outlet, but when it happens for every outlet, we thought it would be a faulty neutral return (from my panel to the transformer across the street. Wiring is underground. Had Con Edison (my electric provider) check it out and I replicated the issue for them, they did some tests and had said it was a faulty neutral so they put a shunt up while they waited to do permanent repairs (said they were going to dig and fix). Now, they tell me it's fixed, but they did no digging.
Current still exists on the water pipe when either the furnace goes on, or when I plug in anything.
a) What is going on?! How do I fix this??
b) If the ground is constantly taking current, does that make sense that it could act as a catalyst to cause the copper pipes to corrode, and thus keep getting pinhole breaks? FYI I had 3 in December this year, and that kind of kicked this into high gear. I had thought that A/C current shouldn't cause corrosion- only DC. Or is it possible that voltage is arcing to the pipe and causing a sudden pinhole break?
//////////////
Some more details:
We know the water pipe gets a leak when I hear a hissing noise in the basement. I currently have a leak but the town is waiting to dig it up until I get this electrical issue fixed. They want to install a dielectric union on the water pipe between their main and my pipe. This makes me nervous because Con Edison told me our zone is coded so that the water pipe is the primary ground. So they would break this path, and thus where would my ground go? The electrician said he could put in 2 more ground rods to make sure that I have a strong ground in place if they do this. I think this is a good idea, but is more a safety backup rather than fixing the problem.
The leaks always seem to show up when it gets cold out, but I don't think they are caused by freezing (since they are 4ft underground). My thoughts are that the furnace circuit is somehow bad and once that starts turning on, it accelerates the process, or starts creating that constant current on the water pipe, and maybe this stresses it till it pops.
I have replaced switches/outlets in the townhouse, as well as a few light fixtures, but I'm pretty positive I know what I'm doing and wired everything correctly. Pretty much one at a time, and just copy the previous wiring. I also do not think I caused this because i found out it happened before I moved in. Also all the lights/switches work, and I used a polarity tester and never showed anything flipped etc. Also there never is any dim/flickering lights or weird situations where the power seems not to be full.
I tried to isolate the circuit by testing different combinations on the breaker. That is how I found out the when the heat goes on, the current always spikes. I also so that when the drier was on, I get a spike, which then led me to test many appliances. Pretty much when anything goes on or is plugged in, and is pulling a load, that amperage shows up on the water pipe.
I've spoken to some EEs at work who I consider very smart. They say most likely that somewhere the neutral is bleeding to ground.
How can I tell if this is Con Edisons responsibility (bad neutral on their side), or if it is on my side somewhere.
Hypothetically if a light fixture wire nut wasn't tight and the neutral was touching the ground somewhere, could that be the cause of this? I thought only that circuit would show the effects of the current bleed onto the ground, or are all the neutrals tied together before the panel somewhere? I'm trying to figure out how every one of my outlets in the house causes current to go on the ground. There is no way they all are wired incorrectly.
I know it's long winded, but this has been quite a stumper. The electrician thought it was a bad neutral on Con Edison's side, but I don't know if he was being lazy and didn't check something on my side. I am capable of checking every switch/outlet in the house to find the problem, but I'd love to avoid that if I don't have to as it will be time consuming and annoying with some fixtures.
Thanks a ton in advance, and looking forward to any help/insight you can share.
-Dan