My wife and I are building a new house in Northern Minnesota on a lot adjacent to our summer lake cabin. The PoCo put in a new pole with a 200 Amp panel and one duplex outlet. (Actually the PoCo moved/replaced an old pole whose location they determined was too far from the pole with the transformer.) The builder ran an extension cord to the building site for construction power.
The building envelope is almost complete. The electrician came out last fall to trench and bury 4/0 aluminum cable (4 wires) from the pole (an unconected loop around the pole) to inside the house where the main panel will be installed. The electrician is planning not to come back until the house is ready for more wiring.
When construction resumes this spring, the doors and windows will go in. Then I will be able to secure the building (lock the doors). In late fall (just before we left), the well contractor moved the pressure tank assembly inside and buried a water line from the pressure tank to the lake cabin.
I made a mistake by not asking the electrician to install the main panel inside, so there is no power inside the new building and no well water going to the cabin.
In order to make construction power available inside and to run a 240 Volt line for the well pump (about 20 feet from the electrical panel area), I am thinking about the following:
(1) Reducing the 4/0 aluminum feeders from the power pole to the status of a "240 Volt extension" since it enters the building underground. At both ends of the 4/0 cable I am tentatively planning to use splicer/reducers (like Home Depot Internet #100190266 -OR- #100126602) to bring the wires down to THHN/THWN-2 AWG #6. I would protect the splices with heat shrink tubing and electrical tape.
(2) At the power pole end I would connect my #6 cable to the feeder lugs. Inside the new house I would connect my #6 cable to a small panel (HD Internet #100194428) with a quad breaker (HD Internet #100186179). This would let me run 240 Volts for a well pump circuit and a couple of 20A @120 V circuits for construction power.
(3) I would maintain separate Neutral and Ground connections at the building panel and would connect the inside ground bar to the slab rebar. I would also secure the excess 4/0 from yanking.
This project would allow us to have water for the building season, greater security when no one is onsite, quickly undo connections when the electrician is ready, but would hardly be Code-compliant. What level of temporary connections are acceptable during construction?
Thanks for you thoughts.
RogerDoger
The building envelope is almost complete. The electrician came out last fall to trench and bury 4/0 aluminum cable (4 wires) from the pole (an unconected loop around the pole) to inside the house where the main panel will be installed. The electrician is planning not to come back until the house is ready for more wiring.
When construction resumes this spring, the doors and windows will go in. Then I will be able to secure the building (lock the doors). In late fall (just before we left), the well contractor moved the pressure tank assembly inside and buried a water line from the pressure tank to the lake cabin.
I made a mistake by not asking the electrician to install the main panel inside, so there is no power inside the new building and no well water going to the cabin.
In order to make construction power available inside and to run a 240 Volt line for the well pump (about 20 feet from the electrical panel area), I am thinking about the following:
(1) Reducing the 4/0 aluminum feeders from the power pole to the status of a "240 Volt extension" since it enters the building underground. At both ends of the 4/0 cable I am tentatively planning to use splicer/reducers (like Home Depot Internet #100190266 -OR- #100126602) to bring the wires down to THHN/THWN-2 AWG #6. I would protect the splices with heat shrink tubing and electrical tape.
(2) At the power pole end I would connect my #6 cable to the feeder lugs. Inside the new house I would connect my #6 cable to a small panel (HD Internet #100194428) with a quad breaker (HD Internet #100186179). This would let me run 240 Volts for a well pump circuit and a couple of 20A @120 V circuits for construction power.
(3) I would maintain separate Neutral and Ground connections at the building panel and would connect the inside ground bar to the slab rebar. I would also secure the excess 4/0 from yanking.
This project would allow us to have water for the building season, greater security when no one is onsite, quickly undo connections when the electrician is ready, but would hardly be Code-compliant. What level of temporary connections are acceptable during construction?
Thanks for you thoughts.