I need to run some 6 Gauge THHN wire (240v) through my house attic. Since it needs to be in conduit, I thought I'd use some 1/2 in. Electrical Nonmetallic Tubing (ENT) raceway tubing that I found a local box store. Is there any reason why that wouldn't work? I haven't come across any limits/restrictions, but just want to see if anyone else had any concerns.


Thanks for your input!


Don
 

· Super Moderator
Joined
·
11,055 Posts
It's 3 wires. Two conductors and a ground.



I need 60 Amps. It's my understand that 6 Gauge Romex NM wire is only good for 55 Amps.


dwan
It is rated for 55 amps, but you can go up to a 60 amp breaker, because they don't make a 55 amp breaker.
What are you feeding?
 

· Electrician
Joined
·
412 Posts
But just for the sake of CEC discussion, would you say it'd be

allowed on a 60 based on T13?
I suppose it would. Table 2 says #6 is rated for 55 amps at a termination temperature of 60°. Table 13 would permit it, but I would have to check the associated rules, at table 13 states "for general use where not otherwise specifically provided for."

Sent from my new phone. Autocorrect may have changed stuff.
 

· Registered
Joined
·
8,252 Posts
It's 3 wires. Two conductors and a ground.
3/4" of any type conduit will suffice.

I wonder what the last person was thinking, laying it out with no conduit. Can't imagine what possessed

I need 60 Amps. It's my understand that 6 Gauge Romex NM wire is only good for 55 Amps.
True, but irrelevant. NM-B cable is forced to use the 60 degree C thermal rating (55A).

THHN running in conduit can generally run at 75 degrees C (65A). But check the connections. If any of those are rated 60C, you must pigtail with a 75C rated splice (like a MAC Block, a good choice for a 6 AWG splice).

When you are provisioning load, you must respect the thermal limit. So in your case if you need to provision 60A, 55A won't cut it; you must do what's required to qualify for 75C operation.

If no breaker is made at that size, you round up to the next available breaker.
 