Joined
·
123 Posts
I'm installing new framing in my basement workshop. I'm using steel studs because I like them. All wiring is going to be in EMT because I'm originally from the Chicago area where wires live in tubes like God intended.
The size of conduit I need determines the width of the stud. The punchouts on the 2.5" studs will only accommodate up to 1/2" EMT, so if I need 3/4" I'll need to go up to 3.625" studs.
I plan on having outlets on two different circuits: one 20A 120V, and one 30A* 240V.
My understanding is that 20A requires 12G wire, and 30A requires 10G wire. I'm assuming THHN wire. The table at E3904.6 of the Virginia Residential code says that 1/2" EMT can hold 9 x 12G or 5 x 10G. If I go with 240V three conductor (i.e., hot, hot, ground -- no neutral), that's 3 (out of 5) 10G, so 60% fill, right? Add to that 3 (out of 9) 12G, or 33%, I figure I'm at 93% fill, right?
Is that how this works? Am I missing something?
(Just to be clear, I'm not doing this wiring myself, just the framing. I just need to figure out the correct conduit size because it needs to be run through the web holes as I put the studs up.)
*My understanding is that 30A is the largest 240V allowed to be installed in the house. Please correct me if I'm wrong. Currently my thirstiest indoor tool is my 3HP bandsaw (15A/240V), but if I were to put a large dust collector on the same circuit, 30A might be pushing it...
The size of conduit I need determines the width of the stud. The punchouts on the 2.5" studs will only accommodate up to 1/2" EMT, so if I need 3/4" I'll need to go up to 3.625" studs.
I plan on having outlets on two different circuits: one 20A 120V, and one 30A* 240V.
My understanding is that 20A requires 12G wire, and 30A requires 10G wire. I'm assuming THHN wire. The table at E3904.6 of the Virginia Residential code says that 1/2" EMT can hold 9 x 12G or 5 x 10G. If I go with 240V three conductor (i.e., hot, hot, ground -- no neutral), that's 3 (out of 5) 10G, so 60% fill, right? Add to that 3 (out of 9) 12G, or 33%, I figure I'm at 93% fill, right?
Is that how this works? Am I missing something?
(Just to be clear, I'm not doing this wiring myself, just the framing. I just need to figure out the correct conduit size because it needs to be run through the web holes as I put the studs up.)
*My understanding is that 30A is the largest 240V allowed to be installed in the house. Please correct me if I'm wrong. Currently my thirstiest indoor tool is my 3HP bandsaw (15A/240V), but if I were to put a large dust collector on the same circuit, 30A might be pushing it...