The rural cooperative POCO installed a new transformer, a new meter, and new 4 awg copper wire in the meter loop (on a pole) to be used as a feeder to the property (after the main service disconnect). The cooperative also advised that the transformer is sufficient for 125 amp service.
I installed a 125 amp main breaker panel immediately below the meter and used 1 AWG from the bottom of the meter to the main service breaker.
According to my review of NEC 310.15(B)(16), I can't find any column where 4 AWG copper is sufficient for 125 amps. So which of the following is the correct scenario:
1. The property will not have 125 amps available due to insufficient cable installed by the cooperative?
2. I am mis-interpreting the correct conductor size for a 125 amp service?
At the moment, I don't know the size of the wires coming from the transformer to the top of the meter. I'll have to check that.