What size copper conductor and what size aluminum conductor would I need for 200 amp run in conduit (PVC). This is from the main disconnect to a main lug. Thanks.
 

·
Super Moderator
Joined
·
9,199 Posts
0000 Al, thwn/ 00 copper/thwn
 

·
Lic Electrical Inspector
Joined
·
1,843 Posts
What size copper conductor and what size aluminum conductor would I need for 200 amp run in conduit (PVC). This is from the main disconnect to a main lug. Thanks.
Is it going to carry the total load for a dwelling unit?
 