Hi forum, my girl has a condo built in 1989, I am trying to help her install an occupancy and dimmer switch into the kitchen with florescent lighting. Lutron makes the switch and in the current switch on the wall we have a black and red (traveler?) wire going to the switch, all white wires are capped together in the rear of the box, the box itself is metal grounded.

My idea:
1. take the black to black on the Lutron
2. take the 2nd black on Lutron to the red wire
3. take the green on Lutron to white (will jump from the 3 white wires currently capped in the box)
4. add grounding wire to box to copper bare wire on the Lutron
5. cap the blue wire on the Lutron

Would this be the correct setup?
 

·
Licensed Electrician
Joined
·
4,352 Posts
What is the model number of the dimmer and what type of fluorescent lighting is in the kitchen?
 

·
Registered
Joined
·
154 Posts
Discussion Starter #3
Hi K_buz,

Lutron Maestro MS_VPS5MH forgot what the lights are called but basic tubed 4-5' length 55 watt I believe.
 

·
Licensed Electrician
Joined
·
4,352 Posts
The dimmer will not work with fluorescent lamps. On top of that, the fixtures would need dimmable ballasts.
 
  • Like
Reactions: HIVOLT

·
Registered
Joined
·
154 Posts
Discussion Starter #6 (Edited)
Oops I wrote dimmer but I didn't mean that, the package states it works on LED or florescent or halogen.

Ok I just called Lutron and they said yes it is a florescent compatible light switch the 5amp ballast indicated that, but the guy said without a true ground wire in my wiring it might work but not guaranteed and they think it will burn it out ie they can't tell me to do it because it's not to code.
 

·
Super Moderator
Joined
·
20,936 Posts
Step 3 is wrong. The green on the sensor is the ground. Connect it to the bare wires in the box not the neutral wires.
 

·
Registered
Joined
·
154 Posts
Discussion Starter #9
I have green to white and it's working

Hi group, I have the green wire to the white cluster and it works are you sure I should take that off and connect to the bare wire ground to the box? I just walked into the area and the occupancy kicked on and just went off. I'm not sure what to do..
 

·
Licensed electrician
Joined
·
13,396 Posts
The green should be connected to the bare or greens, not the whites.
 
  • Like
Reactions: dfphoto

·
Registered
Joined
·
105 Posts
Hi group, I have the green wire to the white cluster and it works are you sure I should take that off and connect to the bare wire ground to the box? I just walked into the area and the occupancy kicked on and just went off. I'm not sure what to do..
Just because it works doesn't make it code compliant and/or safe! Definitely unhook that setup and hook the green and bare from the switch up with the ground wire from the box.
 

·
Registered
Joined
·
154 Posts
Discussion Starter #12
Ok I'll do it your way

Ok not a problem I appreciate your help... I will take the green and combine it with the bare wire but that has to go to the box via a screw.
 

·
Registered
Joined
·
154 Posts
Discussion Starter #13
Ok changed the wiring but..

Hi group, Thank you for the help and support, so I changed the wiring back to green and bare on the Lutron to ground via a screw in the metal switch housing, found an odd behavior of the Lutron. Once I wait 2 min. I can set the time out of the Lutron, so I discovered if I set the Lutron for 1 or 5 min off the unit becomes an occupancy and vacancy switch meaning it turns the light on and off. (this unit is only a vacancy switch via model number) if I choose the longer setting of 30 min to off then the unit is a vacancy only switch. Lutron thinks the unit is bad, wondering if anyone has a comment about it. Thanks again, David
 