I have a question about what to do with Condensor unit wiring. The system I have specifies a minimum circuit ampacity of 30 amps. The unit also states that the minimum HACR circuit breaker should be 40 amps. I understand that this is permitted by article 440 in the NEC.
The unit is wired using 10 guage copper UF wire all the way from the breaker to the disconnect switch outside. The breaker is a Square D QO240 (40 AMP, 2 pole) unit. These are rated as per Square D litterature for use as an HACR breaker. At issue is that the Square D litterature also states that this breaker can accomodate wire sizes 8-2 AL/CU. This appears to be a violation of the breaker's wire termination capacity.
How should this be addressed? Should a short "pigtail" of #8 wire be used at the breaker, then wire-nutted to the 10 gauge wire? Should the breaker be wired using the #10 wire anyway? Should the #10 wire be supplemented by another piece of wire to make it fill the breaker to the range specified, if so how is this determined? Is there a #10 to #8 ferrule which could be used to correct this issue?
The unit is wired using 10 guage copper UF wire all the way from the breaker to the disconnect switch outside. The breaker is a Square D QO240 (40 AMP, 2 pole) unit. These are rated as per Square D litterature for use as an HACR breaker. At issue is that the Square D litterature also states that this breaker can accomodate wire sizes 8-2 AL/CU. This appears to be a violation of the breaker's wire termination capacity.
How should this be addressed? Should a short "pigtail" of #8 wire be used at the breaker, then wire-nutted to the 10 gauge wire? Should the breaker be wired using the #10 wire anyway? Should the #10 wire be supplemented by another piece of wire to make it fill the breaker to the range specified, if so how is this determined? Is there a #10 to #8 ferrule which could be used to correct this issue?