Hello,
Looking for some suggestions. When I went to turn AC on first time this season, compressor turned on, but outdoor fan blade wasn't turning. I replaced the capacitor and a hard start kit, and now the unit is just making a electrical buzzing noise, compressor not turning on. Any suggestions would be great! Thanks
 

· Registered
Joined
·
2,880 Posts
Maybe post a picture of your new wiring. Think you may have something wrong. Be careful because you can burn up your compressor real quick if its wired wrong. Also a breaker could be tripped at this point even though you hear the contactor humming. That power comes from your air handler
 

· Registered
Joined
·
15,740 Posts
If the cap is good, there's a good chance that the condenser fan is dead. To verify, you could test the resistances between the 3 wires of the fan motor. L1-cap should equal L1-L2 + L2+cap. Or just report the readings and wire colours here.

Before any of this, make sure that you have 230V at the contractor.

Cheers!
 