· Hvac Pro
Joined
·
25,116 Posts
No. The plastic will get cold/to the dew point and sweat just like metal. They need to be insulated or have more air moving thru them so they are not so cold.
 

· Registered
Joined
·
2 Posts
Discussion Starter · #3 ·
No. The plastic will get cold/to the dew point and sweat just like metal. They need to be insulated or have more air moving thru them so they are not so cold.
:thumbsup: What do i insulate with?
What does....Have more air moving thru them so they're not so cold mean?

If more cold air were to move thru them wouldnt it get colder and sweat more? Im a little confused on this one. Thanks for your help!:thumbsup:
 

· Hvac Pro
Joined
·
25,116 Posts
Is the unit a horizontal type in an attic? The air temp coming off the cooling coil may be too low from a lack of airflow or too slow fan speed or dirty coil etc. If the air quantity is increased so does the load on the coil and the air temp rises which raises your vent temp above the dew/sweating point. Lots of those attic units use an insulated flex pipe which won't sweat. Metal pipe needs insulating.
 
1 - 4 of 4 Posts