I recently replaced the Copeland Scroll compressor on my 12 year old 12 seer 5 ton Rheem condensing unit. I purged the lines and coils with nitrogen, flushed with Quik-SF, evacuated, broke the vacuum with nitrogen, pressure tested with nitrogen, evacuated and charged. The liquid line drier was replaced and a suction line filter placed. The capacitor and contactor were replaced. On initial start-up the charge was too low and the compressor shuttered and stopped when the suction pressure dropped too low. I added R22, and the system operated appropriately, and cooled well. I planned on checking the system for acid and removing the suction line filter after a week, but after running well for 6 days, the a/c stopped cooling. The breaker (40 amp) had tripped. After resetting the breaker, the compressor will not start, although the fan runs. The breaker did not trip, but it did hum, suggesting high current draw, but I have not put a meter on it yet. Of note, I did not remove any oil from the new compressor, as I felt as though I removed most of the old oil with the flush. Could the compressor be locked from excess oil? Any ideas?
Thanks
 

· Hvac Pro
Joined
·
25,193 Posts
"compressor shuttered and stopped when the suction pressure dropped too low"? How low was it? If it slugged liquid it may have bent the scrolls and you now have a "locked rotor". They damage easily.
 

· In Loving Memory
Joined
·
42,671 Posts
Probably still part of the problem that killed the first compressor.

Suction filter should have been changed within 3 days.

And that is when the system should have been rechecked for acid.

Try putting a hard start on it, to see if it will start again.
If not, consider a new system
 

· Registered
Joined
·
12 Posts
Discussion Starter · #6 ·
The first compressor was wired with 10 guage and a 30 amp breaker, which would trip every month or so. I changed it out to 8 guage and a 40 amp breaker, and found an area in the old wire where a short had developed. I figured that the voltage drop with the old, inadequate wiring, the short, and a 12 year old capacitor contributed to the first compressors demise.
 

· Hvac Pro
Joined
·
25,193 Posts
25 psig for r22 is quite low. below 30 and I would get worried. May have had oil return or circ problem at that low pressure. How long did it run before it did the shutter/stop biz. The old recip compressors could handle a LOT of abuse which the scrolls cannot.
 

· Registered
Joined
·
12 Posts
Discussion Starter · #8 ·
about 10 seconds, off for about 10 seconds,started up again, and stopped after about another 10 seconds, at which time I pulled the disconnect. I added another 2 lbs of R22, and it ran fine with suction 45 psi and high side adjusted to 145 psi at condensor air temp of 65 degrees.
 

· Registered
Joined
·
12 Posts
Discussion Starter · #10 ·
I'm assuming that the compressor shutter stuff was caused by the low pressure switch opening the contactor, and then closing almost immediately when the pressure rose. I'm assuming that the compressor could not start at that point because of the head pressure.
 

· In Loving Memory
Joined
·
42,671 Posts
Is this unit commonly used for cooling during low ambient conditions?

Because letting it run with a low vapor pressure like that, is going to harm the compressor.

plus, if it doesn't have a CCH its going to wash out the compressors oil.
 

· Registered
Joined
·
12 Posts
Discussion Starter · #13 ·
No, its is not normally run at low ambien temperatures. We haven't had much warm weather, and I had the time to replace the compressor on the 65 degree day, so I replaced it then. Didn't want to face the wife's wrath if the A/c wasn't running on the first 80 degree day!:laughing:
 

· Banned
Joined
·
3,705 Posts
It sounds to me like the screen to the TXV may be jammed up with garbage and causing a complete restriction.


Iam not so sure liquid is a culprit because the scrolls raise and separate letting the slug pass thru.
 

· In Loving Memory
Joined
·
42,671 Posts
While a scroll will raise when flooded with too much liquid.

The liquid still washes out oil the same as it does on a recip.

So if ran in a flood back state too long. It can seize them.
 

· Banned
Joined
·
3,705 Posts
While a scroll will raise when flooded with too much liquid.

The liquid still washes out oil the same as it does on a recip.

So if ran in a flood back state too long. It can seize them.
Over temp protection is damn good as the OL is of the inherent type, sensitive to amp and heat. Hard to kill a scroll unless somebody really f's up the install.
 

· Registered
Joined
·
12 Posts
Discussion Starter · #20 ·
I sure appreciate the information, and I'm trying to put it all together. From what I gather, scolls will handle liquid, so my concern about the compressor being locked by excess oil would seem to be without merit. I did not remove any oil from the unit, so I don't think a lack of oil would be the problem. From what I gather on this forum, the scoll compressors are well protected against over load, so I wouldn't expect the compressor motor to have been damaged by the start with inadequate charge. I can't imagine that acid in the system could possibly cause a failure in 6 days. If the TXV were clogged with debris, I would expect the compressor would run briefly until the head pressure built up. The compressor does not run at all. It seems to me the only things left are a defect in the compressor itself(which I seriously doubt), or the compressor ingested debris. I installed a suction filter to prevent this, but is it possible that the filter itself destructed and sent a motherload of garbage into the compressor? I soldered the suction filter on, could I have damaged it with the heat? I didn't remove the suction filter at 3 days because it has been cool, and the unit did not run very much, probably only a few hours a day. I plan on looking at the amp draw next week. Should I try a hard start when it worked perfectly initially, and now won't start at all?
 