· Electrical Contractor
Joined
·
3,370 Posts
Illegal, and DANGEROUS!

This setup imposes one of the current-carrying circuit conductors onto the grounding connection, setting up a potential electrocution hazard. :eek:

But a 3-prong, 3-light plug in tester will show "proper wiring" on such an outlet. :huh:
 

· Licensed Electrician
Joined
·
4,352 Posts
Generally, an inspector does not see how the receptacle is wired. They will stick their plug in tester in and if it reads correct, that is what they assume. On rough inspections, the receptacles are not installed. On final inspections the receptacles are installed and the plates are on.
 

· Registered
Joined
·
1,497 Posts
That is a big dangerous NO NO!

And yes DO check all other outlets.

There is a BIG added safety factor where there is just one neutral ground "bond' (connection) at the main panel, then all the ground wires are run separately to each device/outlet.

Using the neutral as ground can cause the metal frame of a 3 prong appliance to become "hot" should the neutral connection become disconnected, cut by someone drilling a hole in the wall, come loose in a "back-stab" outlet, etc. If you think about this, with the appliance turned on, you are connecting the "hot black wire" to the metal frame of the appliance! The only thing keeping the metal frame near "ground potential" is that neutral wire - lose that wire and ZAP!

And quite common for electrical wires to come loose, be cut, etc.
 

· Registered
Joined
·
1,497 Posts
I looked at the panel and the ground wire is ground at the panel. Any idea why they would do this?
I've seen that done with old homes (non-grounded wiring) and partial rewiring work done. Maybe a new room addition with new wire, then they later replace the main panel and wires going to that. Use the jumper to pass inspection or sell a house before the main panel is replaced.

Or could be a ground wire is broken somewhere.

Or maybe the ground wires are not tied together at a junction somewhere - maybe in the attic.

Easier to place that jumper there than to track down the problem and properly fix it!

If it is the case that was "temporary" until a new panel was installed or the wiring work was completed, then maybe all grounds will now work fine with that and any other jumpers removed?

No telling! Just need to carefully check all outlets. A test that no more jumpers are present would be to remove the ground wire at the panel and see that the outlets no longer have ground with your tester.

That is a more "advanced" sort of electrical work. If you are not comfortable or experienced with working on an electrical panel, might want to have an electrician do that testing for you. Or have him remove the grounds while you go around testing with your tester.

Be safe!
 

· Super Moderator
Joined
·
24,961 Posts
I see a ground wire on the ground screw also. Problem could be a defective neutral connection somewhere that was "repaired" with the jumper. If the circuit still functions with the jumper removed then maybe the problem neutral was repaired and the jumper was never removed.

Remove the jumper and use the receptacle. Check all the other receptacles and see if they have jumpers as well. Remove them if they do.
 

· Registered
Joined
·
19 Posts
Grounded to a separate bus bar? Meaning all the white neutrals are on one bar and the bare ground wire on another?
If not, I would get this fixed first. The reason for this is to eliminate a parallel path for the neutral current.
 

· Licensed Electrician
Joined
·
4,352 Posts
Grounds are required to be bonded with the neutrals in the main panel.
 
  • Like
Reactions: DBW

· Super Moderator
Joined
·
18,318 Posts
Grounded to a separate bus bar? Meaning all the white neutrals are on one bar and the bare ground wire on another?
If not, I would get this fixed first. The reason for this is to eliminate a parallel path for the neutral current.
They can share the same bar in a service panel.
 

· Lic Electrical Inspector
Joined
·
1,844 Posts
Saw it in Camden all the time. Perfect example of what a trunkslammer or amature will do. Illegal and dangerous as hell. Check the entire house or hire an electrical contractor to do it for you.
 