hvac guy says furnance btu too large for house How do I increase air flow in house to stop 61 and 10 codes new rudd furnance ?Or what can I do thanks Brand new unit
 

·
Registered
Joined
·
6,417 Posts
Is the 61 for a blower fault? And the 10 a lockout?
Have them remove the unit and install the correct size if the unit is brand new.
Did you buy this unit yourself and have it installed?
What are the furnace readings from the commissioning report?
 

·
Registered
Joined
·
3,257 Posts
Probably never be right unless you upsize all ducts. Even then the temperature control may be less than desirable.

I assume the HVAC tech has set the fan speed as high as possible and checked the register dampers and any duct dampers for full opening.

You should consult with the manufacturer for any relief they can offer as regulator settings or to burner configuration by plugging off some. It's never going to be right but if you're stuck with it, you'll have to accept that and take whatever measures that make it work without sacrificing safety.
 