circulating pump feeding gv90+ boiler with a built-in circulator
Hello,
I recently replaced a 20+ year boiler with a Weil-Mclain GV90+4. My installer simply replaced the existing boiler with the GV90+4 and did not change any of the existing setup, including a circulating pump on the return line that is continuously circulating into the boiler.
The new boiler has an internal Taco 007 System Circulator that is used to move the water. Is this a problem? In the GV90+ manual I read the following:
"Never install another pump in series with the GV90+ boiler. Forced flow can cause improper operation of the boiler controls. Substantial property damage could result.
Failure to comply could result in unreliable performance and nuisance shutdowns from insufficient flow."
So is my configuration an example of a pump being installed in "series"?
Since the original pump is continuously running what happens when the boiler is not running? Does water enter the boiler? Does the pump need to be removed or relocated to the supply line?
Thanks in advance!

Hello,
I recently replaced a 20+ year boiler with a Weil-Mclain GV90+4. My installer simply replaced the existing boiler with the GV90+4 and did not change any of the existing setup, including a circulating pump on the return line that is continuously circulating into the boiler.
The new boiler has an internal Taco 007 System Circulator that is used to move the water. Is this a problem? In the GV90+ manual I read the following:
"Never install another pump in series with the GV90+ boiler. Forced flow can cause improper operation of the boiler controls. Substantial property damage could result.
Failure to comply could result in unreliable performance and nuisance shutdowns from insufficient flow."
So is my configuration an example of a pump being installed in "series"?
Since the original pump is continuously running what happens when the boiler is not running? Does water enter the boiler? Does the pump need to be removed or relocated to the supply line?
Thanks in advance!