I found out that outlet lost power after Circuit was overloaded by plugging too many heaters. Believing that resetting the breaker would restore the power, I reset the breaker and the breaker above tripped. Still no power on the dead Circuit.
A properly wired MWBC will have the two hots on opposite legs of the panel. The neutral will only see the difference in current, not the additive of current.Make sure if this is a house with Romex or BX cable that the two circuits are not going to a three wire cable like a cable with a black, red, white, and a bare wire if so you are overloading the neutral (white) wire if so the wire will get to hot and trip the breaker.
Sent from my Pixel 3 using Tapatalk
°Could melting happen at an unused outlet when overload happened?