The contractor proposes to replace an old system and to install
Trane gas furnace TUD1B060936, a new Trane cased coil 4TXCB036 and a new Trane SEER 13 condensing unit 4TTB3036. Also, he proposes to charge it with R410 refrigerant, while other contractors recommend R-22 because the lines are too small (small diameter). What is the consensus?

None of the contractors have followed anything like the ACCA standards that indicate quality installation, such as making the Manual J caloculation, give a performance guarantee as to what the house temperature will be relative to the outside temperature. Is that typical? All this in the Philadelphia, PA area.

I need all the advice I can get to protect myself since I donot know how to evaluate the estimates and contracts.
 

·
GC/Master Plumber/Mech
Joined
·
1,517 Posts
While any pro here will tell you to get a man J done there isn't a single pro here that hasn't done a change out without doing the man j and I am guilty of it too. I'm not trying to make excuses but it does happen.

Most utility companies wil do it free of charge for a home owner and this wil help you in keeping a contractor honest.

As far as line sets. Sometimes it is hard to replace the line set, finished basement so we will flush the lines but, if the line set that is in place is smaller than what is needed for the new system then the HO and contractor need to come up with a plan to replace.

As far as going with R-22 because the lines are to small then the contractor is not taking into consideration that the system you have now is more than likely less than 10 SEER and the new will be 13 SEER or higher so the lines need to be replace. Especially the high side line to the 3/8" line.

Go with R-410a because R-22 is being phased out and the warranty will be less with 22. Trane has gone to a 10 yr warranty but you or the contractor must register the system within 90 days of install or warranty drops to 5 yrs

So go with 410a and try to increase the line set size
 

·
Registered
Joined
·
702 Posts
The line size specifications for your proposed system should be available on the trane web site. Many times you will only see a percent or two difference unlesss the lineset is unusually long. I take it you are replacing a 3 ton system?
 