Discussion Starter · #1 ·
I installed my own furnace and A/C last fall and hired a tech to braze and startup the A/C side of the system. He used a seat-of-the-pants method to add refrigerant to the system at startup. I suspect it is overcharged, so I was about to hire a tech to come out and check the charge using subcooling.

My first question is about how far off could the SC number be and still be considered acceptable? I do not know for sure the manufacturer's SC listed on the rating plate, but it is likely in the 10- to 12-degree F range. Should I expect the SC be withing +/- 2- or 3-degrees F or tighter?

Second, my only fear is that the system has been overcharged. My 2.5-ton unit, according to the product data sheet, comes with 11-lbs of 410, which includes charge for a 15-ft lineset. It recommends adding 0.6-oz for each additional foot of lineset. My lineset is 25-feet, which means the tech should have added about 6-oz. So, apparently the right amount of total refrigerant for my system would be 11 lb - 6 oz. If my installing tech, in fact, added 1-lb of charge (not 6-oz), would a tech I am about to hire, with average technical skill running a SC test, find the SC to be out of tolerance? In other words, about how much would the system have to be overcharged, relative to the recommended 11 lb - 6 oz, for the SC number to be out of tolerance? Would it even have been a problem if the original installing tech had not added the 6-oz needed?

Ultimately, I am concerned that whatever tech I hire to check the SC is sufficiently knowledgeable to do the work properly and adequately adjust the charge. Will the average tech be very capable of doing what I need done? If not, how does one "delicately" ask about a tech's understanding of the work prior to having them do the work?

Thanks.
 

· Banned
Joined
·
1,107 Posts
Your system comes with 11lbs of 410A.
You should post model and serial of condenser.
lbs sound WWWAAAAY too much 410A in a 2 1/2 ton system.

If you are trying too have a little fun at the expense of this board, I'd advise against it. you won't get any usable advice if you are.
 

· Registered
Joined
·
73 Posts
Discussion Starter · #3 · (Edited)
Your system comes with 11lbs of 410A.
You should post model and serial of condenser.
lbs sound WWWAAAAY too much 410A in a 2 1/2 ton system.

If you are trying too have a little fun at the expense of this board, I'd advise against it. you won't get any usable advice if you are.
I am absolutely not looking to yank anyone's chain. I got the info from page 3 of this document:

http://www.docs.hvacpartners.com/idc/groups/public/documents/techlit/pds165a.18.1.pdf

It appears to show the charge for a 2.5 ton unit as 11-lb. In the installation manual for the same 165A condenser, it lists the standard length at 15 and 0.6 oz for each foot greater than 15.

On all of my previous post I have been most appreciative of the help I have received here, so I am confused as to how my straightforward post would have been interpreted as satire, except for the fact that I may have misread the table.

It sounds like I have misinterpreted this table. Please help me understand what the actual charge is for this condenser. Thanks.
 

· Registered
Joined
·
1,407 Posts
Why you suspect it is overcharged?
Did the technician used a digital scale to charge system?

Basically you add the refrigerant according to the manual and then add more according to the size line set length. The subcooling is checked after the system is stabilized for fine adjustments.
 

· In Loving Memory
Joined
·
42,671 Posts
According to that doc. You are correct, it has a factory charge of 11 pounds. Not uncommon for high SEER equipment to hold a large amount of refrigerant.

Is your 16 SEER or more?
 

· Registered
Joined
·
128 Posts
It's also possible that he charged it to manufacturer's superheat specs, but didn't use a full pound. A lot of companies won't bill you in increments of a lb, in other words the required 6oz may have been added but the bill reflected a full pound.
 

· In Loving Memory
Joined
·
42,671 Posts
Thank you "been", so I am not nuts! Yes, with my coil combination, the ARI rating is 16-seer.
You install or work on a few "high" SEER units. You get use to seeing large amounts of factory charge.

If you don't work on a lot of "high" SEER, it sounds like too much of a charge.
 

· Registered
Joined
·
2,362 Posts
A few extra ounces might show up as a +1 degree of SC and the charts usually state +/-1 degree so it should be good to go. High SEER units run way less SC then the old 10-12 SEER did. I helped the installers set up a 21 SEER and the charging chart called for a 2 degree SC.
 

· Registered
Joined
·
73 Posts
Discussion Starter · #12 ·
Why you suspect it is overcharged?
Did the technician used a digital scale to charge system?

Basically you add the refrigerant according to the manual and then add more according to the size line set length. The subcooling is checked after the system is stabilized for fine adjustments.
When I said seat-of-your-pants, I mean he hooked up the tank, opened the valve for a little bit, let some refrigerant run in, and then closed the valve. No weighing, no SH or SC before or after. Therefore, since it only appears to have needed 6-oz more than the base charge (11-lb), I suspect that it is overcharged, but do not know for sure.
 

· I'm Your Huckleberry
Joined
·
5,885 Posts
I hear furnace and a/c but does the evaporator coil have a txv or a fixed orifice metering device such as the normal piston? If piston (or old school cap tube) then charge superheat, not subcool.

And make damn skippy both your inside and outside coils, evaporator and condenser coils, are clean and that your static pressures are correct or there is no reason in checking your charge in the first place.

Industry standard and manufacture design, if you want it done right.
 

· Hvac Pro
Joined
·
25,214 Posts
You install or work on a few "high" SEER units. You get use to seeing large amounts of factory charge.

If you don't work on a lot of "high" SEER, it sounds like too much of a charge.
So True, Just look at the literal physical size of a larger SEER unit. The condensor coils are huge/have more feet of tubing and the evap coils are a lot bigger too. Therefore they hold more refrigerant. And as every good tech knows the bottom coil or 2 of the condensor holds liquid refrigerant so the quantity needs to be there to fill them up.:thumbsup:
 

· Registered
Joined
·
73 Posts
Discussion Starter · #16 ·
I hear furnace and a/c but does the evaporator coil have a txv or a fixed orifice metering device such as the normal piston? If piston (or old school cap tube) then charge superheat, not subcool.

And make damn skippy both your inside and outside coils, evaporator and condenser coils, are clean and that your static pressures are correct or there is no reason in checking your charge in the first place.

Industry standard and manufacture design, if you want it done right.
Yes, this has a Bryant cased coil with a built-in TXV, so that's why I was asking about SC. To your second point, the condenser and coil were new when installed last fall, so they are both still very clean and the static at 1100 cfm with the furnace running is 0.56, so that should be fine.

So, back to my original question, the guy I hired casually added some R410a to account for the increased lineset length of 10-feet. If he overshot by, say, 10-oz and put in a full pound, would the SC be off by more than one or two degrees? BTW, the rating plate calls for an SC of 13-deg F.

As an aside, how does the manufacturer know the capacity of the evaporator you plan to match with your condenser? If I installed a matched, but oversized evaporator (3.5-ton coil with a 2.5 condenser), would that also require additional charge to be "full"?

Thanks.
 

· Banned
Joined
·
1,107 Posts
You install or work on a few "high" SEER units. You get use to seeing large amounts of factory charge.

If you don't work on a lot of "high" SEER, it sounds like too much of a charge.[/quote

You are right Been, my bad. we can't even give away 16 seer in this neighborhood (Tax credit or no. We are just now getting a few call back to work at some of our auto related industries) and I have yet to install one so I have some catching up to do.
 

· Banned
Joined
·
1,107 Posts
Yes, this has a Bryant cased coil with a built-in TXV, so that's why I was asking about SC. To your second point, the condenser and coil were new when installed last fall, so they are both still very clean and the static at 1100 cfm with the furnace running is 0.56, so that should be fine.

So, back to my original question, the guy I hired casually added some R410a to account for the increased lineset length of 10-feet. If he overshot by, say, 10-oz and put in a full pound, would the SC be off by more than one or two degrees? BTW, the rating plate calls for an SC of 13-deg F.

As an aside, how does the manufacturer know the capacity of the evaporator you plan to match with your condenser? If I installed a matched, but oversized evaporator (3.5-ton coil with a 2.5 condenser), would that also require additional charge to be "full"?

Thanks.
Can't speak for Bryant but ICP and Nordyne both say +/- 2 or 3*f degrees.

I would probably think it would be the same for your equip.
 

· I'm Your Huckleberry
Joined
·
5,885 Posts
Forget the length of the line set. Superheat and subcooling go hand in hand, txv or not. There are considerations such as ambient temperatures and wet bulb temps which equate to formulas to derive a system's proper target charge so again, forget your lineset length. That is over and yesterday and not important any longer. Proper cfm is as well as those other considerations so with your slightly higher than average static pressure I'm going to assume you are close to nominal as you are going to allow your system to be. I should ask where were the measurments taken to come up with .56" anyways but I won't.

Anywho, here's some good info you can read and study. All systems pretty much act the same, the same rules apply. Good luck!!

http://www.udarrell.com/ac-trouble-shooting-superheat-subcooling.html

http://www.hvacsalesandsupply.com/Linked%20Documents/Tech%20Tips/Proper%20System%20Charging.pdf
 

· Hvac Pro
Joined
·
25,214 Posts
Carrier recommends 350 cfm/ton from a chart I saw on a newer MXA high efficiency unit. You may want to be around 900-1000 cfm for better performance with their units. Probably best to get a Carrier/Bryant tech from a large well established company to check it. Ask for the senior tech and hope he knows his stuff. If it is a Carrier furnace that info should be with the setting fan dip switches section in the install manual AND on the sticker on the door with the wiring diagram if you have an ECM motor.
 