Hey Im working a water cooled heatpump (cruise air) I am not used to adding freon in low temp. Im in heat mode and it is working, but the compressor is really really hot. I tought I over charged it so I pulled it all out and started with 2 pounds. I think the think is 1.5 tons but that seems huge for a 40 foot boat. There is no charging chart or even a name plate.
Here are my pressures and temps:

od temp 50F
high side 240 and 175F
true suction 50 and 53F
indoor temp 56F
evap temp 93F
vent output 88F
water temp is about 65f

when I shut the system off it is 110 psi seems high to me for 50f DB.

Do these numbers sound right?

Thanks for the help
 

· Registered
Joined
·
201 Posts
Discussion Starter · #5 ·
Im not sure what you mean, that is what I was using to calculate superheat and subcooling. That is what I am not sure of, in ac mode that is how I calculate it, is it not the same for heat mode.

Superheat is the difference of the evap temp (or converted suction psi) - the temp reading at the suction line, right?
 

· Registered
Joined
·
201 Posts
Discussion Starter · #8 ·
this is a Marine system it is made by cruise air. There is no name plate, or charging charts. I see what you're saying now about the subcool, but there is lots of superheat which makes me think its under charged. but when the system is off it is 110 PSI which makes me think it is over charged on a 50 degree day. with no subcool wouldn't that mean its not rejecting the heat inside?

once again thanks for all your help
 

· Items wanted: Time
Joined
·
195 Posts
your off temp is because of the water temp, don't worry about it. Charge the thing to 15 degrees subcooling. All else being good, you should be fine. Subcooling is you high side saturation - liquid line temp.
 

· Registered
Joined
·
201 Posts
Discussion Starter · #13 ·
once again correct me if I'm wrong because I'm sure that I am, but I thought when an AC system has been all for sometime and all the pressures are equalized the psi converted to temperature should be the ambient temperature
 

· In Loving Memory
Joined
·
42,671 Posts
once again correct me if I'm wrong because I'm sure that I am, but I thought when an AC system has been all for sometime and all the pressures are equalized the psi converted to temperature should be the ambient temperature
The water is your ambient.

In heat mode the indoor coil is your condenser, and the coaxial is your evap.
 
  • Like
Reactions: wetbar

· In Loving Memory
Joined
·
42,671 Posts
A system can be under charged, and still have the same pressure as the ambient sat temp. Tells you nothing about the charge.The system must be running to tell if its charged right or not.
 