I have a Carrier 2 stage mid efficiency furnace model 58CVA/CVX. I would like to know if I can reduce the duration of the low heat/fan cycle from the current 15 minute to 2 or 3 minutes. This will allow the high heat/fan cycle to come on quicker. We are a 2 storey house with the furance in the basement. Currently, the furanace works as follows:
- furnace fires up for about 1 minute
- low heat/fan starts and continues for 15 mines
- high heat/fan starts and continues for 10 minutes until the temperature is attained
- then furnace changes to low heat and runs for about 10 minutes
- furnace shuts off and the low fan continues for about 1 minute and then shuts off.
I need the high fan to blow air to the top floor of the house. thanks.
 

·
Banned
Joined
·
17,158 Posts
You really need a thermostat with a Differential setting for multi-stage furances. Also, it really does not matter where the furnace is, it is where the thermostat is located, if there are enough returns available on the second story.
 

·
Administrator
Joined
·
42,246 Posts
A jumper can be put across W1 and W2 at the stat or furnace. This could make things worse, as the first floor will also heat up quicker. Your heating problem is more likely an undersized duct system problem.
 