Yes, another pulsing lights thread! I've read all of them and am still at a loss, months and months of troubleshooting and can't figure it out.
Background: brand new house < 2 yrs old, 150A 240V service, any type of light will pulse, on/off a dimmer, LED or incandescent, and on any circuit. One leg 116 the other leg 120.
It took a while to figure out the culprit was a Ninja coffee maker. Every couple seconds it must be keeping some of the water hot so its always pulsing the lights where they dim and go back (I learned not to use the word flicker, there is no loss of power). So the lights go from a 10 to a 9 to a 10 to a 9 all day, it's like a mini strobe fest.
As I was about to write it off as a bad coffee maker (or as another thread so eloquently put it, cheap Chinese java pot), I found I'm able to re-create the same problem using one of those electric tea kettles that heat water rapidly (pulls about 10A when you turn it on). So I turn on the kettle and the lights go from say a 10 to a 9 and it holds the loss of light while the kettle is on, then when I turn the kettle off it goes back to a 10. If the lights are on a dimmer and dimmed low forget about it, the pulsing is much worse and rapid like the light is struggling to stay alive while the kettle is on.
So it's not isolated to a specific appliance or a circuit (same behavior on a dedicated kitchen GFCI 20A or a standard 15A), I can plug the tea kettle in just about anywhere and visibly see the light impact to surrounding circuits. Strange it doesn't seem to happen with microwaves, a/c, hairdryers, or garbage disposal, these have more normal behavior, where you turn a/c or disposal on it will pulse once and everything is normal while it runs, so turning it off has no impact.
Electricians have been out and tightened all the neutrals, POCO came out and did a triple deep freezer simulation on the 240 without any voltage drop. This was all before I figured out what caused the issue.
So I had electrician out and we would flip the kettle on and off and watch the voltage drop 3 volts on one leg and rise 1-2 volts on the other. He said something about harmonics? We went outside where an exterior outlet is next to service meter and we watched the same behavior there. He thinks I should call POCO out again and show them the voltage fluctuation at the meter and suggest thicker gauge wire be run to transformer.
I'm reading nobody will care about this level of voltage drop and it's normal. I'm out about $300 between 3 sparky visits and getting the right person at DTE that actually cares to look at this stuff takes a LOT of phone calls. They just see a clean 240 on their end and walk.
I suppose I could show DTE how the kettle behaves at the service entry point but I'm trying to minimize the continued back and forth.
Anything else I can try or communicate to move this along? I've never seen this level of sensitivity in a house so it's a bit surprising, especially a fairly new house, it just seems odd to write this issue off, I do have some other pulsing issues upstairs that I suspect are related to this load sensitivity? voltage drop? harmonics?
Any thoughts on where to go from here? Much appreciated!
Background: brand new house < 2 yrs old, 150A 240V service, any type of light will pulse, on/off a dimmer, LED or incandescent, and on any circuit. One leg 116 the other leg 120.
It took a while to figure out the culprit was a Ninja coffee maker. Every couple seconds it must be keeping some of the water hot so its always pulsing the lights where they dim and go back (I learned not to use the word flicker, there is no loss of power). So the lights go from a 10 to a 9 to a 10 to a 9 all day, it's like a mini strobe fest.
As I was about to write it off as a bad coffee maker (or as another thread so eloquently put it, cheap Chinese java pot), I found I'm able to re-create the same problem using one of those electric tea kettles that heat water rapidly (pulls about 10A when you turn it on). So I turn on the kettle and the lights go from say a 10 to a 9 and it holds the loss of light while the kettle is on, then when I turn the kettle off it goes back to a 10. If the lights are on a dimmer and dimmed low forget about it, the pulsing is much worse and rapid like the light is struggling to stay alive while the kettle is on.
So it's not isolated to a specific appliance or a circuit (same behavior on a dedicated kitchen GFCI 20A or a standard 15A), I can plug the tea kettle in just about anywhere and visibly see the light impact to surrounding circuits. Strange it doesn't seem to happen with microwaves, a/c, hairdryers, or garbage disposal, these have more normal behavior, where you turn a/c or disposal on it will pulse once and everything is normal while it runs, so turning it off has no impact.
Electricians have been out and tightened all the neutrals, POCO came out and did a triple deep freezer simulation on the 240 without any voltage drop. This was all before I figured out what caused the issue.
So I had electrician out and we would flip the kettle on and off and watch the voltage drop 3 volts on one leg and rise 1-2 volts on the other. He said something about harmonics? We went outside where an exterior outlet is next to service meter and we watched the same behavior there. He thinks I should call POCO out again and show them the voltage fluctuation at the meter and suggest thicker gauge wire be run to transformer.
I'm reading nobody will care about this level of voltage drop and it's normal. I'm out about $300 between 3 sparky visits and getting the right person at DTE that actually cares to look at this stuff takes a LOT of phone calls. They just see a clean 240 on their end and walk.
I suppose I could show DTE how the kettle behaves at the service entry point but I'm trying to minimize the continued back and forth.
Anything else I can try or communicate to move this along? I've never seen this level of sensitivity in a house so it's a bit surprising, especially a fairly new house, it just seems odd to write this issue off, I do have some other pulsing issues upstairs that I suspect are related to this load sensitivity? voltage drop? harmonics?
Any thoughts on where to go from here? Much appreciated!