· Registered
Joined
·
7 Posts
Discussion Starter · #1 ·
I have been blowing the 3 amp fuse when my ac is turned on. It runs fine with the heat on. The fault code is for a short in the 24v wiring. I checked my ac unit outside and couldnt find and shorts. I also installed a new thermostat this winter so i double checked the wires going into it and they all seem to be correct. Thanks in advance for your help it has been 88 degrees the last 2 days here in cincinnati and getting a little toasty...:furious:
 

· Hvac Pro
Joined
·
25,116 Posts
Disconnect the 2 AC wires from outside where it attaches to the circuit board in the furnace and turn the AC on. If it does not blow then the outdoor wiring REALLY is shorted. Very common to get chewed by dogs/rodents and hit with weed whackers or dried up and insulation bare from the sun and UV rays.
 

· Hvac Pro
Joined
·
25,116 Posts
Either wire going outside could be shorted. You just removed part of the circuit , C common but it proves that there is a short downstream from the furnace. It could be shorted inside the outdoor unit in the electrical box or possibly the contactor is sticking and drawing too much current. 95% chance is the damaged wire scenario.
 

· Hvac Pro
Joined
·
25,116 Posts
If it blows instantly then there is a short. I have never had a contactor draw too much current and have done this for many many yrs but I have heard it is possible. Thermostat wires can be shorted along ductwork, have staples pulled thru them so you may have to run a new wire to find out or call a Pro. Should have #18 gauge wire and not any thinner stuff like telephone wire.
 

· Registered
Joined
·
7 Posts
Discussion Starter · #13 ·
ok yesterday when i was supposed to take off the blue com wire to check for a short i took off all 3 blue wires. realizing my mistake today i started with the blue wire that ran to the ac unit and it was fine it ended up being a problem with the thermostat so i have about 2 feet of slack that i have pulled thru the wall and havent found any broken wires. im ready to pull out my hair
 