My Carrier 58 MCA has an abnormally long igniter warm-up time. Here's what happens: The thermostat calls for heat - the furnace starts working, churning, sometimes for 30 minutes without a call for gas...then it calls for gas, it lights, hot air blows for 2-3 minutes then shuts off. The furnace immediately starts working again, churning again for a short time, then, it calls for gas, it lights, and hot air blows for as long as it takes to give the thermostat what it wants. This is a high efficiency set-up, it just seems terribly inefficient to me - any ideas?
 

· Items wanted: Time
Joined
·
195 Posts
It could be in the flue pipe intake or exhaust, in the pressure switch tubing, in the pressure switch, in the condensate collection box, in the condensate piping, in the condensate trap. But I would check the voltage across the pressure switch before checking any of them. If you have a voltage meter it is pretty easy to do.
 

· Registered
Joined
·
195 Posts
Check diagnostic light to see if any codes come up during long start up time.Probably get a code 31 .Move the wires on press switch alittle.If problem clears up, replace pressure switch because older metal ones commonly fail on this unit due to vibration of ID motor.
 

· Registered
Joined
·
19 Posts
Discussion Starter · #6 ·
I'll check it - I suppose the proper voltage is noted in the owner's manual. If it's too low it will indicate a blockage? I would be fairly confident to disconnect hoses and check for debris - I don't see myself getting too invasive. I've earned my diy stripes...but, I worry about messing with the gas - my kids sleep here:.)
 

· Registered
Joined
·
19 Posts
Discussion Starter · #7 ·
Check diagnostic light to see if any codes come up during long start up time.Probably get a code 31 .Move the wires on press switch alittle.If problem clears up, replace pressure switch because older metal ones commonly fail on this unit due to vibration of ID motor.
Now that's my kind of advice - jiggling wires! Definitely within my skill set. Will do. Thank you!
 

· Items wanted: Time
Joined
·
195 Posts
with voltmeter set to ac and your leads one on each terminal of the switch. small motor in burner compartment will spin and there should be no voltage reading if furnace is working correctly. This means switch is closed and there is no potential difference across the switch. it that little motor is spinning and you see 24 volts (give or take a couple volts) then you have a blockage somewhere.
 

· Registered
Joined
·
19 Posts
Discussion Starter · #10 ·
I got a code 31

OK, I jiggled some wires and did a error code check: as predicted by you fellas, it's a code 31. I don't have a voltometer: If I were to first try clearing any potential blockages...using the attached photo to point me in the right direction, where would I start? I busted out the schematic to find out how to do the code check....
I can try and find the various tubes....but would appreciate some guidance.
Is this risky business? Or, is it just a matter of un-doing a tube, shaking it out and re-connecting?
And, I noticed some moisture as seen in the more close-up photo. Is this a sign of something?
 

Attachments

· Registered
Joined
·
195 Posts
Looks like you have a plugged condensate trap.The white thing with hoses going to it.Best way to clean it is remove and flush with hot water.You could try and blow it out if you have compressor.Have towel ready because there will probably be alot of water coming out of larger rubber hose when you pull it off trap.
 

· Registered
Joined
·
195 Posts
If you want to remove trap you have to take bottom panel off, two screws usually, then you will see bottom part off trap.Should have a rubber hose that drains to outside off furnace.Loosen clamp andpull hose off.Then remove three hoses on top side, the big one will have water pouring out.Then squeeze two tabs on top side and swing trap to the left and out.Flush with lots of hot water till no more garbage comes out.I usually fill and shake it over and over till water comes out clean.
 

· Registered
Joined
·
19 Posts
Discussion Starter · #19 ·
OK, cleaned that condensate as recc'd. It wasn't terribly dirty...ran clean very quickly. And, the larger tube that you said would gush water....dripped just a little. Don't know if that's significant. I did "blow" all of the tubes to clear them while I had them off.
What should I try next?
 