Nope. Too much heat, and not a combined unit. Inspector will call you on it, especially if you don't have another heating source (such as forced air) in the room.
1 X 15A Circuit for your GFCI receptacle and Lights
1 X 15A GFCI circuit for the rest of your heating if the manufacturers instructions require a GFCI or EPD Breaker.Otherwise a regular 15A is good to go.
62-110 Branch circuits
(1) Branch circuit conductors used for the supply of energy to heating device sets shall
(a) be used solely for such heating device sets; and
(b) have an ampacity not less than that of the connected load supplied.
(2) For the purpose of this Rule, an approved unit that combines heating with ventilating or lighting equipment, or both, shall be considered to be a heating device set.
(3) Notwithstanding Subrule (1), where a heat lamp is not the sole source of heat, it shall be permitted to be used in a luminaire approved for the purpose or in a box-mount-type luminaire, where the luminaire is supplied from a general-use branch circuit
62-114 Overcurrent protection and grouping (see Appendix B)
(1) Every heating fixture, heating cable set, heating panel set, or parallel heating set having an input of more
than 30 A shall be supplied by a branch circuit that supplies no other equipment.
(2) In buildings for residential occupancy, two or more heating fixtures, heating cable sets, or heating panel
sets shall be permitted to be connected to a branch circuit used for space heating, provided that the branch
circuit overcurrent devices are rated or set at not more than 30 A.