41 - 57 of 57 Posts
You talking to me?
Of course you can. Why would it matter the OCD will protect the wiring. They dont make a receptacle for EVERY amperage. so you do what you have to do.
then how why would they bother with 210.23. As you said, regardless of the load applied, the OCPD would protect the conductors yet they specifically state that in no case shall the load exceed the circuit rating.
and what does making a recep for every amperage have to do with anything?
210.23 is exactly what it says, as far as your second question, what receptacle would you install for a 85 amp welder? And what code section would allow it?
Lets keep it really simple, ever see a 40 amp range receptacle?
What would be the purpose of installing a 20A single receptacle on a 15A branch?
Any device requiring a 20A receptacle would also require a 20A circuit, or else it wouldn't have the 20A plug in the first place.
Having the 20A receptacle on a 15A circuit would only serve to confuse and frustrate the user of the equipment. He would connect the device to the 20A receptacle, only to have the 15A breaker trip after some time.
And then, why permit the 20A single receptacle on a 15A circuit, but not when there are two or more outlets on the circuit, or not when the receptacle is a duplex?
Let's see if I get a reply from NFPA on this.
okay, so why install a 50 amp receptacle on a 40 amp breaker? Your so confusing the issue.
You talking to me?
;200774]210.23 is exactly what it says,
yes, a limitation that states you cannot connect a load larger than the circuit to the load and installing a 20 amp recep on a 15 amp circuit would allow that.
what kind of welder?
Nope but what does this have to do with the question at hand?
who cares? I gave the load.
Everything, like I already stated a million times, what code section allows a 50 amp receptalce on a 40 amp breaker? O'yeah, the same one that allows a 20 amp receptacle on a 15 amp breaker, you guys need to just read what it says and get over it.
Discussion Starter #47
My post was in no way directed at you, but at KE2KB, hence the quote before I responded, but feel anyway you want. :) Next time before you react to something, take a second to realize what is being said and to who. It will do us both a favor, I give my free time and knowledge for free so you can save a buck, so dont rant on me about nothing.
Chris,
On behalf of myself and every other dummy that maliciously performs maintenance on his home in order to cheat you out of a dollar; thank you very much for the information! You have proved yourself to be very knowledgeable. Please leave your address with my secretary and she will send you a dollar. :) No hard feelings.
UAW SKILLED TRADES
If they didn't want a 20 amp receptacle on a 15 amp individual branch circuit then why is a 20 amp receptacle configured to accept a 15 amp power cord (Nema 5-15) or a 20 amp (Nema 5-20)? If this was a big issue they would just configure it to accept 20 amp cords only.... Or they would make it as a duplex only. There is some degree of common sense for portable cord and plug equipment or fixed in place cord and plug equipment. I can just as easily overload a 20 amp branch circuit serving multiple outlets with 15 amp appliances ( two hair dryers for example) as a 20 amp individual receptacle on a 15 amp rated branch circuit. In the end the breaker protects the wire. Also consider the fact that 14 awg copper has an ampacity of 20 amps but can only be breakered at 15.
Food for thought....if the branch circuit is a dedicated cord and plug motor load (with internal overload protection) could I not install a 20 amp breaker on that 14 awg and a 20 amp single receptacle? Assuming an flc of 16 amps. Read 430.42(C)
You talking to me?
=chris75;200789]who cares? I gave the load.
because it makes a difference
You posed this question:
you said nothing of a code section. You asked if I had ever seen a 40 amp range receptacle. Your response above seems to imply a diffferent question.
You talking to me?
hush stubbie, I'm having too much fun screwing around with chris. I acknowledged my mistake long ago but figured since he was willing, I would just keep him running.
Oh, and Chris, the welder response; it does make a diff, there is more than one type of welder and the calcs a different and there were several questions that followed. The Ieff, duty cycle, quantity of welders supplied, and probably a few other items. The recep minimum ampacity rating is based upon the circuit conductor ampacity and to calculate that, there are questions to be answered. An 85 amp welder requires a circuit less than 85 amps. You ought to know that.
You defend your point well.:thumbsup:
UAW SKILLED TRADES
Hi Nap
Just had to get my 2 cents in on a thread like this. Chris is a pretty sharp cookie and I don't win too many disagreements with him.. I'm sure he is having as much fun as we are with this.
DIY'er
I got us started in a discussion just like this over on terry love's site by pointing out that a duplex outlet in a photo that a electrical inspector posted was illegal. Not at first realizing this was a violation, After some discussion, the inspection did agree that the outlet was in fact a violation.
The discussion starts here at post #52 if your intrested:
http://www.terrylove.com/forums/showthread.php?t=24875&page=3
Jamie
Jamie
I was involved in that one as well. :thumbup:
You talking to me?
Hi Nap
I hope so.
My apologies to you Chris if I ruffled the feathers. I was being a bit arrogant to start, you corrected me and at that time I figured I was going down fighting, or having fun.
for that
Hopefully no hard feelings.
Jamie
Why point out the same pointless argument on a different site? Chris is right.
DIY'er
Sorry if I offended you. It appeared to me that several people where having trouble understanding this and were confused by it.
I felt the thread on the other site was a good teaching example, as it showed how even a veteran code inspector was confused with the issue.
I was just attempting to be polite and helpful to those that had trouble understanding the issue. Not trying to cause any problems.
Merry Christmas
Jamie
Merry Christmas
Jamie
Sorry if the post came off offensive. The other site just points out another example of how the code is misread by some people. I find it funny that goofball with all the "accreditations" didn't know the difference between a single and a duplex receptacle.
41 - 57 of 57 Posts