I have a 4 ton Trane 15i condenser paired to a 5 ton ADP coil with a 100k btu XV95 2-stage variable speed furnace.
When it was installed the blower speed dip switches were set at 400CFM per ton and the resulting external static pressure was over 1.0 even though the nameplate called for 0.5 max heating (and no mention for cooling.)
After I discovered the high esp the unit was adjusted to run at 80% of blower speed or 320/ton. I pretty much ran all last summer this way with no issues except that my esp is still high at ~0.75.
I know the dips can be set to 350/ton which would mean my airflow would be 80% of 350 which is 280/ton.
Does anyone see a problem with the air flow being that low (280CFM/ton)?
What are the risks?
The indoor coil has a TXV.
Thanks in advance for your insight
Key1
When it was installed the blower speed dip switches were set at 400CFM per ton and the resulting external static pressure was over 1.0 even though the nameplate called for 0.5 max heating (and no mention for cooling.)
After I discovered the high esp the unit was adjusted to run at 80% of blower speed or 320/ton. I pretty much ran all last summer this way with no issues except that my esp is still high at ~0.75.
I know the dips can be set to 350/ton which would mean my airflow would be 80% of 350 which is 280/ton.
Does anyone see a problem with the air flow being that low (280CFM/ton)?
What are the risks?
The indoor coil has a TXV.
Thanks in advance for your insight