Njuneer
Joined
·
1,064 Posts
Discussion Starter · #1 ·
I was just talking with a design tech that I know and was comparing voltage drop data. I was surprised how far apart we were and it seems he uses a different method for the calculation. Mine seem to arrive at the same number as about any calculator online but his were up to 3X as much voltage drop.

Just curious what formula and tables references you use? Let's leave the actual application and and loads and such out of it and concentrate on the actual value. I would also like to know if you guys look mostly at 90c for service entrance wire or if you build for 75c?


Thanks
 

·
Super Moderator
Joined
·
15,485 Posts
Were you using the total length of the circuit which is the out and back distance or only out? Were you using the same design load?

Your wire needs to be sized based on the lowest rated part of the system. You will not find terminations rated 90C, but the wire can be derated from the 90C ratings.
 

·
Njuneer
Joined
·
1,064 Posts
Discussion Starter · #3 · (Edited)
Because of the length of run, wire heat is not as much an issue as Vdrop. Loads are being calculated phase - phase with equal Vdrop between them so of course it would double.

I am more or less looking for hard calculations here.

As for the temp rating, I thought one could use a higher current rating but lower temp rating to offset operating higher temp wire? Is that not the case? Obviously the NEC will limit the current in the conductor to a safe level anyway and right now our wires are looking to run about 55C but Vdrop is a concern. I am working back through the physics of it and going to compare the NEC book to actual periodic table data just too see if there are engineered margins there. Sometimes too many compounded margins ends up getting ridiculous IMO.
 

·
Lic Elect/Inspector/CPO
Joined
·
369 Posts
See 210.19 A1 FPN #4

The note says that the 3% is just for a branch circuit. For the Feeder and the Branch circuit its a total of 5%
If you supply the information, I will do a calc and we could compare results.
 

·
Njuneer
Joined
·
1,064 Posts
Discussion Starter · #5 ·
Thanks!

Example would be:

4/0 Aluminum 240V 1ph
500ft from transformer to load
150A load


Another is 500mcm Al, 240V 1ph
500ft as well
300A load

Oh, these would both be underground in conduit installations so I am figuring 15-20C ambient.
 

·
Registered
Joined
·
9,639 Posts
We do not use temperature when figuring voltage drop. However when choosing the wire size needed to avoid temperature problems (in conduit, in free air, kind of insulation, etc) we might already come up with a wire size large enough to not suffer excessive voltage drop.
 

·
Sparky
Joined
·
706 Posts
Thanks!

Example would be:

4/0 Aluminum 240V 1ph
500ft from transformer to load
150A load


Another is 500mcm Al, 240V 1ph
500ft as well
300A load

Oh, these would both be underground in conduit installations so I am figuring 15-20C ambient.

#1 i get -15V(6.25%), to get under 5% i show needing 300kcmil AL, for 3% i show 500kcmil AL


#2 i get -12.72V(5.3%)to get under 5% i show needing 600kcmil AL, for 3% i show 1 run of 900kcmil AL, 2 runs of 500kcmil AL, 3 runs of 300kcmil or 4 runs of 250kcmil AL
 

·
Njuneer
Joined
·
1,064 Posts
Discussion Starter · #8 ·
Huh, that is yet another value. do you happen to have the equation that was used to calculate that?

One that seems to be floating around the net that I am not sure I agree with is (2*L*R*I)/1000 That produces 12.06% for the 4/0 using .0804/K for resistance. The NEC books I think is .1 ohms for 4/0 so there is a little discrepancy there.
 