I have a 100 amp breaker panel feeding an electric furnace through ~ 30 feet of aluminum cable specified as "PRIORITY 3C 2AWG AA8000 1C 4AWG AA8000 TYPE SE STYLE R XHHW-2 600V XIPE (UL) 2008 05323 FT".

When the furnace is running, the outside jacket of the cable reaches 120 degrees F. Is this indicative of a problem? From what I've been able to look up on the cable I believe it is OK for the 100 amp service.

Any advice is appreciated.
 

·
UAW SKILLED TRADES
Joined
·
5,341 Posts
I have a 100 amp breaker panel feeding an electric furnace through ~ 30 feet of aluminum cable specified as "PRIORITY 3C 2AWG AA8000 1C 4AWG AA8000 TYPE SE STYLE R XHHW-2 600V XIPE (UL) 2008 05323 FT".

When the furnace is running, the outside jacket of the cable reaches 120 degrees F. Is this indicative of a problem? From what I've been able to look up on the cable I believe it is OK for the 100 amp service.

Any advice is appreciated.

I hope that breaker panel is dedicated to the furnace and is fed from service equipment panel that is 200 amps or so.

That temp. is not excessive XHHW-2 is rated 90C or 194F

The wire size would suggest a amperage requirement of the furnace to be in excess of 65 amps.
 

·
Registered
Joined
·
3 Posts
Discussion Starter #3
Thanks for the quick reply. The breaker panel is dedicated to the furnace and it's connected directly to the meter as a separate 100 amp service.

The furnace manual says the max current draw could be 97 amps. It's a 22.5KW unit.
 

·
Semi-Pro Electro-Geek
Joined
·
3,403 Posts
#2 Aluminum XHHW-2 is good for 100A if the equipment is rated for 90*C terminations. Which it's almost certainly not. So it's good for 90A. The furnace is a bit of an overload for that cable in that installation, but I would not change it.
 

·
Electrical Contractor
Joined
·
1,994 Posts
I have a 100 amp breaker panel feeding an electric furnace through ~ 30 feet of aluminum cable specified as "PRIORITY 3C 2AWG AA8000 1C 4AWG AA8000 TYPE SE STYLE R XHHW-2 600V XIPE (UL) 2008 05323 FT".

When the furnace is running, the outside jacket of the cable reaches 120 degrees F. Is this indicative of a problem? From what I've been able to look up on the cable I believe it is OK for the 100 amp service.

Any advice is appreciated.
I also agree with mpoulton but you could always get someone in there to check to make sure all the connections are good and maybe check how much it's drawing. Just a few bucks to have the extra insurance that everything is checked over and OK.
 