Discussion Starter · #1 ·
Please help. My Bryant plus 90 furnace (model 350 MAV) goes through the ignition cycle, but does not light. It provides a fault 31 code. I have verified operation of pressure switch based on directions in my owners manual. I hace cleaned the ignitor rod, vacuumed the burner ports, and cleared all obstructions and vent restrictions. The inducer motor works. Does anyone have any ideas? Thanks.
 

· Registered
Joined
·
5 Posts
Discussion Starter · #3 ·
The code is 31. The manual states that this is the pressure switch. There is no smell of gas. The gas valve does not open--it doesn't get to this point in the cycle. The start cycle initiates, but the ignitor fails to glow. The gas valve will not come on.
 

· HVAC / Plumbing
Joined
·
1,801 Posts
check the vent for obstruction.... check that the vaccun line is clear.check that the vent motor is pulling vaccum... You can jump vaccum switch at the 2 wires & see if it comes on . If it's bad...vaccum switches don't cost much
 

· GC/Master Plumber/Mech
Joined
·
1,517 Posts
Have seen build up in the port where the hose off the pressure switch connects at the inducer or collector.
 

· GC/Master Plumber/Mech
Joined
·
1,517 Posts
First I would like to thank you for not keeping an American working and not supporting our economy.

Second if you are not sure then BUY American.

BONG!!!!
 

· Registered
Joined
·
5 Posts
Discussion Starter · #11 ·
Plumber 101: I agree. Americans should make it a point to buy "American". I bought an American made home in the United States--and unfortunately the builder (or previous homeowner) chose to purchase a foreign furnace. What was I supposed to say...I'll take the home, but only if you pull out the furnace?
 

· Registered
Joined
·
5 Posts
Discussion Starter · #13 ·
Fixed. It was the igniter assembly. The pressure switch initially tested fine with the manometer, but after installing the igniter something went wrong. So, I then tested the switch to make certain that the draft inducer was working properly--and it was. When I troubleshooted the control center everything ran fine--the test sequence indicated that the problem wasn't with the control center. To make a long story short, the problem was entirely my fault…I left my husband alone in the basement with the furnace. He was inadvertently switching the hoses to the pressure switch. This is why sometimes the furnace would run fine (during test mode) and then it would stop working. The last time he did this I asked how it was that he could not read the numbers on the meter, but had no problem reading the positive sign on the switch. We then realized what had happened. I feel silly posting this, but perhaps someone will learn from this mistake. Thanks to everyone for all the help.
 

· HVAC / Plumbing
Joined
·
1,801 Posts
Fixed. It was the igniter assembly. The pressure switch initially tested fine with the manometer, but after installing the igniter something went wrong. So, I then tested the switch to make certain that the draft inducer was working properly--and it was. When I troubleshooted the control center everything ran fine--the test sequence indicated that the problem wasn't with the control center. To make a long story short, the problem was entirely my fault…I left my husband alone in the basement with the furnace. He was inadvertently switching the hoses to the pressure switch. This is why sometimes the furnace would run fine (during test mode) and then it would stop working. The last time he did this I asked how it was that he could not read the numbers on the meter, but had no problem reading the positive sign on the switch. We then realized what had happened. I feel silly posting this, but perhaps someone will learn from this mistake. Thanks to everyone for all the help.



Glad to hear you got it fixed:yes:
 