They are telling you not to use a 2pole transfer switch. They want you to use a 3pole transfer switch. A 3pole switch will isolate the house neutral ground bond, if wired properly.
The reason behind it is safety. If you have 2 neutral ground bonds in the system and something goes wrong with the neutral, the ground will carry the neutral current. This would energize the generator frame.
It serves the same purpose as the never do a neutral bond ground in a subpanel rule.
The reason behind it is safety. If you have 2 neutral ground bonds in the system and something goes wrong with the neutral, the ground will carry the neutral current. This would energize the generator frame.
It serves the same purpose as the never do a neutral bond ground in a subpanel rule.