Hello. I have an 80 amp circuit. Dual pole 80 amp breaker, number 4 wire, 50 foot run. I am running 67 amps on this circuit. Everything works fine until it gets hot out side. Then the breaker starts tripping. If I reset it later, when it has cooled down outside it works fine. What would be the proper fix for this?
 

·
Semi-Pro Electro-Geek
Joined
·
3,403 Posts
Circuit breakers trip via two mechanisms. On very high current faults, there is a magnetic device that trips the breaker instantly. On lower-current faults, a little element inside heats up and trips the breaker. If the breaker is artificially heated to too high of a temperature, the thermal trip mechanism can activate from the heat without there being an overcurrent. That sounds like what's happening. This is almost always caused by a loose connection on the breaker. It may be the breaker's connection to the panel bus, or a wire connection to the breaker. Remove the breaker and look for any signs of overheating on the bus tab or the fingers on the back of the breaker. Make sure it seats snugly on the bus when you reinstall it. If it feels loose or shows signs of heating, sand the bus tab clean (POWER OFF!) and replace the breaker. Also check the connections to your cable. Loosen and re-torque the connections, using anti-oxidant if it's aluminum.
 

·
Electrical Contractor
Joined
·
3,368 Posts
An 80 Amp breaker is not sufficient to handle a 67 Amp continuous load.

Now you know why.
 

·
Semi-Pro Electro-Geek
Joined
·
3,403 Posts
An 80 Amp breaker is not sufficient to handle a 67 Amp continuous load.

Now you know why.
If the load is continuous, then the breaker and wire should be sized for 125% of 67A, or 84A. However, an 80A breaker is one which will carry 80A forever without tripping. Only a current above 80A will trip it. Tripping at 67A is abnormal and indicates a heating problem.
 

·
Licensed Electrical Cont.
Joined
·
7,829 Posts
What is this circuit feeding?
There's the $64 dollar question. :icon_rolleyes:

The cable is NOT tripping the breaker. What the cable is connected to is. :whistling2:
 

·
Licensed Electrical Cont.
Joined
·
7,829 Posts
If the load is continuous, then the breaker and wire should be sized for 125% of 67A, or 84A. However, an 80A breaker is one which will carry 80A forever without tripping. Only a current above 80A will trip it. Tripping at 67A is abnormal and indicates a heating problem.
KB, this is correct. It is NOT tripping because there is 67A on an 80A breaker. :thumbsup:
 

·
Registered
Joined
·
5 Posts
Discussion Starter · #9 ·
Hey guys, thanks for all the responses. The wire is 4 3 romex ( copper). I checked all connections and the are tight. The bus gar does not look abnormal in any way. I am running only lighting on this circuit. Digital ballasts. The main pannel where the breaker is, is on the east side of the house an gets hit by the sun all day. As soon as it gets above 85 outside it trips. So is this whole line to small for 67 amps?
 

·
Registered
Joined
·
1,324 Posts
What type of wire, beyond AWG is it?
Scof1212 said:
Hey guys, thanks for all the responses. The wire is 4 3 romex ( copper).
My question was based on OP's answer above. It's Romex (or, NM-B), which is listed at 60°C in the ampacity chart. BUT, I suppose this isn't a factor, since 60°C = 140°F.

Feel free to dog me, cause I'm still learning :eek:
 

·
Registered
Joined
·
1,324 Posts
My question was based on OP's answer above. It's Romex (or, NM-B), which is listed at 60°C in the ampacity chart. BUT, I suppose this isn't a factor, since 60°C = 140°F.

Feel free to dog me, cause I'm still learning :eek:
However, #4 NM-B (Romex) is listed ashandling only 70 amps, isn't this correct?

I'm using the ampacity chart from Cerro Wire: http://www.cerrowire.com/default.aspx?id=46
 

·
Registered
Joined
·
756 Posts
If you are using an ordinary ammeter to measure the 67 amps, that only measures the peak of the waveform and divides by root(2) to get the rms. A ballast creates significant harmonic content. Measure the amps with a true-RMS meter and see what you get. The true-RMS value is what the CB responds to.

Mark
 

·
Electrical Contractor
Joined
·
3,368 Posts
... The main pannel where the breaker is, is on the east side of the house an gets hit by the sun all day. As soon as it gets above 85 outside it trips. So is this whole line to small for 67 amps?
You have to account for ambient temperature correction, it would seem.

The sunlight is heating up the guts of your panel, making the breaker think it is overloaded, even though it may not be. Since many breakers have thermal trip mechanisms, this may be your culprit. That, and a weak breaker, since it is carrying a heavy continuous load to begin with.

Did you replace the breaker? Is it possible to split that circuit into more, smaller circuits?
 

·
Electrical Contractor
Joined
·
3,368 Posts
KB, this is correct. It is NOT tripping because there is 67A on an 80A breaker. :thumbsup:
In theory, perhaps. Real-life experience has shown that a high continuous load such as this can, over time, cause a breaker to weaken and eventually trip out. Add in some hot sunlight and voilà! Nuisance tripping. As the OP has discovered.

I would never connect such a lighting load in this manner, as problems would eventually develop ....
 

·
Registered
Joined
·
5 Posts
Discussion Starter · #15 ·
Yeah, I don't have a true Rms meter. So is the overall consensus that I shoul upgrade to 100 amp breaker and 2 3 romex? Or will that not cut it either? Or should I go get one of those meters first?
 

·
Registered
Joined
·
5 Posts
Discussion Starter · #16 ·
Also yes I did replace the breaker. And it is not possible to split it. It is the last open space on the main panel.
 

·
Semi-Pro Electro-Geek
Joined
·
3,403 Posts
Also yes I did replace the breaker. And it is not possible to split it. It is the last open space on the main panel.
If you've replaced the breaker and gotten the same result, then I would conclude the load is probably above 80A RMS and your meter is not displaying it properly. You'll need to measure the actual load, or at the very least add up the current ratings of all the devices on the circuit. You'll probably need a feeder and breaker rated for more than 100A, since your existing load seems to be more than 80% of that already.
 

·
Learning by Doing
Joined
·
3,156 Posts
Question of Fact: what kind of lighting needs this kind of juice and wire gauge?
 

·
Semi-Pro Electro-Geek
Joined
·
3,403 Posts