DIY Home Improvement Forum banner
1 - 8 of 8 Posts

· Registered
Joined
·
2,554 Posts
Discussion Starter · #1 ·
Have 1p 20a breaker that keeps tripping. I turn it on and it buzzes for a second or two and shuts to off. I know it possible the breaker could be bad but the panel/breakers are fairly new. Anything else I can troubleshoot/check? Thank you. It does indicate the rooms it serves on the panel schedule.
 

· Super Moderator
Joined
·
18,344 Posts
A slow trip like that sounds like a high resistance short. This may be an Easter egg hunt to find the cause.
 

· Registered
Joined
·
2,554 Posts
Discussion Starter · #5 ·
What's the circuit used for? Lights? Receptacles? Anything plugged in? Sounds like something is just overloading the circuit. That's what they are there for.
Nothing at all plugged in. No loads on circuits. Switches that feed receptacles and regular unswitched receptacles. We just gutted house(not sure if it was working prior) so I check if any wires nicked but all looks good.
 

· Registered
Joined
·
2,842 Posts
You will need to go to a receptacle near the start of the circuit and disconnect the wires. Test each pair of black and white with a continuity tester (everything unplugged from all on the circuit). That will tell you which direction to look for a short ( continuity means a short).
 