first I want to say thank you to anyone who replies to help mw out I really appreciate it because I've been wracking my brain over this. I just bought a 4 family flat partially renovated and it has a brand new Rheem 40 gal electric hot water heater. Everything was hooked up except the wires to the breaker. At the heater has 10 gauge wire, black to black, red to white, and ground to the grounding screw. Then it runs in conduit all the way to the box and we hooked up the black and white wires to a double pole 30amp breaker and the ground to the ground screw. We filled it up until it was full and flipped on the breaker. Waited 30 minutes, nothing, 1 hour, nothing. Thinking my next step is to check power is going to the unit, any other suggestions to check? Thank you
 

· Electrician
Joined
·
1,404 Posts
Is your breaker sitting on both phases in your panel? Quickest way to test is to see if you get 240V at the tank. if you have 120V from each wire to ground but not 240V between the two wires you will need to move the breaker.
 

· Registered
Joined
·
35 Posts
first I want to say thank you to anyone who replies to help mw out I really appreciate it because I've been wracking my brain over this. I just bought a 4 family flat partially renovated and it has a brand new Rheem 40 gal electric hot water heater. Everything was hooked up except the wires to the breaker. At the heater has 10 gauge wire, black to black, red to white, and ground to the grounding screw. Then it runs in conduit all the way to the box and we hooked up the black and white wires to a double pole 30amp breaker and the ground to the ground screw. We filled it up until it was full and flipped on the breaker. Waited 30 minutes, nothing, 1 hour, nothing. Thinking my next step is to check power is going to the unit, any other suggestions to check? Thank you
Darren's prolly right. Your 2 pole breaker has to be across 2 different phases. Could be as easy as moving the breaker, but if you're not qualified, hire someone. Don't try to be a hero. The white wire is a code violation but not a huge safety issue. My concern with that would be, if they did that wrong, what else did they do?
 

· Registered
Joined
·
13 Posts
Discussion Starter · #6 ·
Thanks for your replies, it has produced no heat at all, I was thinking to check the breaker when I get back so ill let you know on that, and as for the white wire is it not ok to use a white as power if you put electric tape on last 4 inches to mark it live, I see that alot here on building we work on
 

· Super Moderator
Joined
·
24,990 Posts
It is only OK to use white for power when cable is used because cable comes with black and white wires. If yo have conduit the wires pulled is up to you and you need to use two coloured wires for hot. Normally you would use black and red but any colour other than white, grey or green is acceptable.
 

· Super Moderator
Joined
·
18,353 Posts
If the old WH worked the breaker should not be an issue. They can fail but it is rare.

What does the thermostat say?
 

· Registered
Joined
·
13 Posts
Discussion Starter · #11 ·
Its a brand new water heater never used I ran new wires to it hooked up to breaker and have 120v of I test one wire with ground and 240 testing the black and red together going to drain the unit refill purge for r and re hook up electric
 
1 - 18 of 18 Posts