My heating system is losing pressure and now requires topping up daily via the filling loop in order for the boiler to work. I have a Vaillant Eco boiler with a large tank in the loft. The filling tap is located next to the tank in the loft. There is a pressure gauge next to both the tank and the boiler. The last Engineer to have a look gave up and just left the filling tap on slightly to maintain pressure (for some reason it fills to 1.5 bar and then stops filling so the PRV never kicks in). I have resorted to simply leaving the filling tap on slightly but since it stops at 1.5 bar you would not know it is even on (I know this is not ideal, not least because the inhibitor will have been thoroughly diluted). If I turn off the filling tap, pressure drops to zero within a few hours.
I can't find any leaks anywhere in the system and the PRV is not leaking which I think rules out both the PRV being faulty and also the expansion chamber as this would present via the PRV right? This, I have read, leaves the possibility that the Heat Exchanger has a pinhole or crack through which system water is escaping via the condensate pipe. This theory is possibly supported by the fact that recently the condense hose was leaking water and had to be replaced (A new hose and trap have been installed) - could this leak have been caused by a problem with the Heat Exchanger and hot escaping water?
I want to confirm whether the issue is in the boiler (i.e. the heat exchanger) or somewhere else in the system. To do this, I believe I can top up the pressure, then isolate the boiler by shutting off the flow and return valves. After a few hours, if the pressure in the boiler has dropped I will know the issues lies there, but if it hasn't and only drops when I turn the valves back I will know the issue is elsewhere in the system?
Four questions?
1) Does the Heat Exchanger seem the likely culprit given what I have said?
2) Am I understanding the check procedure correctly?
3) How do you shut off the flow and return valves on the boiler (is it just a case of rotating 90 degrees with a screw driver)?
4) Does anyone see any other issues or anything I may have overlooked from the details I have given
I can't find any leaks anywhere in the system and the PRV is not leaking which I think rules out both the PRV being faulty and also the expansion chamber as this would present via the PRV right? This, I have read, leaves the possibility that the Heat Exchanger has a pinhole or crack through which system water is escaping via the condensate pipe. This theory is possibly supported by the fact that recently the condense hose was leaking water and had to be replaced (A new hose and trap have been installed) - could this leak have been caused by a problem with the Heat Exchanger and hot escaping water?
I want to confirm whether the issue is in the boiler (i.e. the heat exchanger) or somewhere else in the system. To do this, I believe I can top up the pressure, then isolate the boiler by shutting off the flow and return valves. After a few hours, if the pressure in the boiler has dropped I will know the issues lies there, but if it hasn't and only drops when I turn the valves back I will know the issue is elsewhere in the system?
Four questions?
1) Does the Heat Exchanger seem the likely culprit given what I have said?
2) Am I understanding the check procedure correctly?
3) How do you shut off the flow and return valves on the boiler (is it just a case of rotating 90 degrees with a screw driver)?
4) Does anyone see any other issues or anything I may have overlooked from the details I have given