my furnace is a Goodman gmp100-3 rev b. When my blower comes on it fills my house with cold air for about a minute, then i hear the burner kick on. It takes it even longer to heat my house since all the cold air was pushed in for a minute. I've made sure the thermostat is configured for gas furnace properly. I was hoping to get some help with this and will appreciate any tips and troubleshooting given. Thank you very much.
 

· Registered
Joined
·
9 Posts
I had a similar issue. I have a gas furnace. I found that the thermostat (a Lowes bought Honneywell) was configured for an electric furnace.

For some reason, this caused the blower to kick on for about a minute before the burner.

Switching the thermostat to gas solved the problem.

On older thermostats, there are usually jumpers on the back for this. On new ones, there is generally a reset button, and then a series of "first time use" questions.
 

· flipping slumlord
Joined
·
5,124 Posts
bought this house last may... it's always done this... furnace says 1993
I've had a big list of things to get done around here
and i'm just getting around to this one.
Squeaky wheel's are like that.

The blower isn't supposed to start until the burner has been on for a while
(and it should stay on for a while after the burner goes off too).

It might just be the $5 sensor it might be the $200 board the sensor relates to. Either way...

Some manuals to read:

http://www.getbookee.org/goodman-gmp100-3-manual/
 

· In Loving Memory
Joined
·
42,671 Posts
i just bought this house last may, but yes it's always done this since ive started running the heat last septemberish. I've had a big list of things to get done around here and i'm just getting around to this one. the furnace says 1993
As others said, check thermostat configuration. Also, that model is known for popping its crimp rings. May want to watch if the flames start to jump around when the blower starts after you gt it to come on when it should.
 

· Registered
Joined
·
3 Posts
Discussion Starter · #8 ·
i should have put this in the first post. The thermostat is configured correctly for gas furnace, i've already gone through their support to make sure i wasn't missing anything. I'll start browsing through that manual thanks, any other thoughts?
 

· In Loving Memory
Joined
·
42,671 Posts
Short in the thermostat wires. Lower aux limit tripped(look on blower housing).
 