Look for a red button on the motor itself. Push it to see if it resets. Will also need to reset safety control again after resetting motor.
is this on just a water heater or boiler with coil? electric going to the burner? wall switch turned off by mistake?So lastnight was doing dishes and noticed no hot water. Thought maybe out of oil but not. Checked and reset had tripped so I press reset and nothing!! No pump no motor Nada and its been -20° here!!! Luckily got a small Amish box heater keeping main rooms 65° but need a furnace.
So red light on on reset and nothing at all happens when reset pushed then after 30-45 seconds trips reset again
some of the newer controls have lockouts after you press them once or twice..I think if you turn off the power to the unit for a few minutes it resets the control, but you still need to find out why the burner wont stay running..It is a furnace with baseboard and also does hot water as well. Wall switch is on green and red zone lights are on and red reset light is on but when reset is pressed nothing happens except the button popping again in 30-45 seconds
hold down red button for 30 to 40 seconds to unlock control...that should do it..but you still have to find out reason burner quit in first place..I shut power for a few min and still the same so I'll try shutting it for 5+min and see if that makes a did