1 - 7 of 7 Posts
Hi all,
I am in the planning stages of a basement bathroom addition. My question relates to the design of the curcuit. I know that each bathroom must be on its own 20A circuit. Is it okay to run 12/2 from the panel to a GFI outlet and then from that GFI to another outlet and then on to power a switch for the light and fan? The bathroom will be combined with the laundry area, which has its own circuit for the washer & dryer. The reason I ask is that I saw the post below on a different site:
In a given bathroom
  • On a per-bathroom and a per-lavatory basis
    • Without regard to the size of the bathroom (i.e., ½-bath, 3/4 –bath, etc.)
    • Without regard to how close one lavatory is to another
    • Without regard to whether the mount requires piercing a mirror, moving a rack, etc.
  • At least 1 dedicated, ground fault circuit interrupter (GFCI, or GFI) shall be installed
    • Which circuit shall be rated 120V/20A and
    • Which receptacle shall be rated 120V/20A
    • Which installation shall be proximate to and within 3 linear feet of each bathroom lavatory and
  • This circuit shall be dedicated to that receptacle only and to no other application whatsoever
    • There shall be no branches in these dedicated circuits for fans, lights, heaters, or anything else, i.e., wire the rest separately
Thanks:thumbup:
Licensed Pro
If you dedicate the circuit to just that bathroom, then you can have the receptacles and the lights/fan on the same circuit. You need to have a GFCI protected receptacle within 3ft of the outside edge of the lavatory.
Unless the light/fan is within a shower area and requires GFCI protection, I would run the circuit to the switch first, then to the receptacle. That way a tripped GFCI will not put you in the dark.
And the receptacle does not need to be a 20A, a 15A will do.
Discussion Starter #3
It is just for that bathroom. When you mention within 3 feet of the outside edge, what do you mean?
Licensed Pro
I mean that the receptacle has to be located adjacent to the sink, within 3ft of the edge. If you have two sinks, a receptacle has to be located within 3ft of each sink. Usually a receptacle mounted between the two will satisfy this.
Discussion Starter #5
If the one near the sink edge that I install is an outlet that is downstream from the GFCI outlet but is wired so as to be protected by the GFCI outlet, would that be acceptable? Or, does the actual GFCI outlet need to be the one next to the sink?
Licensed Pro
The requirement is that it be GFCI protected; there is no requirement that it be a GFCI receptacle. The actual GFCI can be anywhere in the bathroom (except in the tub/shower area) or a GFCI breaker.
Discussion Starter #7
Thanks. I'm actually only putting in a 1/2 bath/laundry combo:
pedestal sink
laundry tub/basin
toilet
recessed can
vanity light
fan
Very helpful. Thanks!
1 - 7 of 7 Posts
