Hello fellow DIY'ers! I am finishing my basement which was already roughed out for plumbing including a sewage ejector pit. I know the sewage pit needs a dedicated vent of its own and so I have two related questions:

1) There is a 2" pipe coming through the floor joists above directly above the sewage ejector pit. It looks to be intended as the vent pipe for this pit. How can I tell/trace where this vent pipe actually vents? (and if anything else ties into it?)

2) The new bathroom is roughly about 7'-8' from where the sewage pit is located. Do I need vents for each of the fixtures (toilet, sink, shower) AND the sewage pit, or just venting the pit good enough for code?

2A) Assuming the rough in was done right when the house was built, perhaps the roughed in fixtures are already vented? If so, how can I tell?

I'd appreciate any and all ideas and thoughts!
 

· Registered
Joined
·
6,652 Posts
You must vent the bathroom fixtures to the vent left for the sewage ejector pump. Without a picture I cannot tell how the bathroom was installed. But usually all you need vent is the lavatory sink.

You should also pull the pump out to make real sure it is a grinder pump and not a storm water sump pump. If all it was handling was a floor drain it is a good possibility they went the cheap route on the pump.
 

· Premium Member
Joined
·
13,105 Posts
Sewer pumps do not always need to vent out seperately. Use the capped vent for the pump and in the ceiling, run the lav vent to it. This will complete your venting.

The ejector pump line should tie into a vertical 4" building drain using a wye branch connection
 

· Registered
Joined
·
6,652 Posts
Vent the lavatory sink you should be good to go. Next question is where is the pump going to discharge to? You need 2 pipes by the sump one for the pump one for the vent. Keep the lav vent 42 inches or higher above the floor and it must be run so it is totally self draining.
 

· Registered
Joined
·
4 Posts
Discussion Starter · #6 ·
Thanks guys!

1) The main discharge line runs along right above the sewage pit (can't really see it in the picture) so should be good there.

2) I keep reading that the sewage ejector pump has to have a dedicated vent line for code? Thoughts on this for Georgia (Forsyth County to be exact)?

Also, if I vent the sink/lav drain line, is it a correct assumption that the toilet and shower are tied to that vent below the concrete?
 

· Registered
Joined
·
4 Posts
Discussion Starter · #8 ·
Gotcha! Thanks Ghostmaker and ePlumber!! For closure, you guys are right on the money... (not that you needed to be told that) I reached out to the senior plumbing inspector for my county and he validated exactly what y'all already said. All good, that is again!
 