Discussion Starter · #1 ·
I have a 50 amp GFCI breaker in my main panel. this is for a sub panel in our backyard that has nothing connect to it currently. When I flip the breaker on it trips. I verified there was no continuity between the two black power wires. I disconnected those from the breaker And so the only thing connected to the breaker at the main panel is the neutral wire and the pigtail that goes to ground. When I turn the breaker on it still trips. Is this breaker bad?
 

Attachments

· Registered
Joined
·
3,257 Posts
I'd remove it and clean it up good. If there is any crud on the terminals, it could be faulting to ground. If no joy then, it will need replacing. I suppose there is a good reason for having that type of breaker on sub panel feeders???
 

· Registered
Joined
·
8,260 Posts
I would expect 90% chance the problem is a ground fault at the other end of these wires. Although you unhooked hots, neutral is still connected and that can ground fault too. I would unhook neutral.

If it still trips, then I'd clean up the breaker good and plenty and see if that clears it. There is a lot of dirt getting into that panel; see if you can address that. Dirt + moisture = leakage.
 