My GOODMAN GSZ140421KA HVAC UNIT (MFG. OCT 2015) stopped blowing cold on Thursday.
I called the largest HVAC outfit in my hometown for a troublecall. Its 90 degrees out.
Tech arrives next day. Tells me to turn off the unit (from my phone, I have a nest controller) He hears the compressor "humming" trying to kick on, then quits. repeats a couple times. Using a clamp, he tests the line and its "drawing 10 amps" during the 'humming' periods. He installs a (presumbably used) run/start capacitor from his truck into the unit. No change. He also notes some brown heat marks on the defrost board.
Written Diagnosis: Failed compressor & degraded defrost board. $2200 to replace.
???
I request and pay for a second opinion from the second largest outfit in town.
It's saturday now. Same process, only now this new tech's (presumably used) capacitor starts the compressor (!) but the shroud fan still won't turn. I suggest we bump the fan blade with a stick? He agrees. The fan comes up to speed. Unit blows cold. House now back down to high 70's. Nice! (NOTE: This time my unit was cold from being left off a full day)
His Diagnosis: Bad Fan- orders $110 fan to arrive tuesday. Says the cap is fine.
Something still doesn't seem right to me. He insists the used cap he leaves in the unit is fine (even though it needs to be bumped to start the fan - not kidding)
Frustrated that I got what seems like two bad diagnosis/techs, I read up on hvac (I was a navy radar tech, never an HVAC tech) and refresh my memory on how to test fan motors and capacitors.
I ohm out the fan. Heres the readings:
Black to Purple: 29.1
Black to Brown: 66.7
Purple to Brown: 94.1
So, 1 to 2 ohm off.
My understanding (based on some youtube videos) is if Bk2Pu+Bk2Br=Pu2Br or very close, then the fan is good.
None of the 3 terminals show shorted to capacitor exterior btw.
Also, FAN spins freely when not energized. I feel, hear, see no signs of bad/degraded bearings. I think the reason the fan didn't work for the first tech was it was overheated and was in overtemp shutdown mode.
Capacitance Readings on the 5/45uF 440V dual capacitor.
Common to Fan:0 uF (instead of 5uF +/-5%)
Common to Herm: 28 uF (Instead of 45uF +/- 5%)
MY diagnosis: Bad capacitor (no doubt), fan is fine (?)
Two questions:
1) IS MY FAN BAD ALSO, BASED ON THE SYMPTOMS AND READINGS GIVEN?
2) I ordered a new cap off Amazon. Fan and Cap dont arrive till tuesday (its sunday). CAN I SAFELY RUN THE AC WITH A CAPACITOR THAT READS 0uF/28UF VS 5uF/45uF if I just bump start the fan, and let it to cool all day. ( Ill shut it off at night) Will this damage my unit in any way?
Thank you!
I called the largest HVAC outfit in my hometown for a troublecall. Its 90 degrees out.
Tech arrives next day. Tells me to turn off the unit (from my phone, I have a nest controller) He hears the compressor "humming" trying to kick on, then quits. repeats a couple times. Using a clamp, he tests the line and its "drawing 10 amps" during the 'humming' periods. He installs a (presumbably used) run/start capacitor from his truck into the unit. No change. He also notes some brown heat marks on the defrost board.
Written Diagnosis: Failed compressor & degraded defrost board. $2200 to replace.
???
I request and pay for a second opinion from the second largest outfit in town.
It's saturday now. Same process, only now this new tech's (presumably used) capacitor starts the compressor (!) but the shroud fan still won't turn. I suggest we bump the fan blade with a stick? He agrees. The fan comes up to speed. Unit blows cold. House now back down to high 70's. Nice! (NOTE: This time my unit was cold from being left off a full day)
His Diagnosis: Bad Fan- orders $110 fan to arrive tuesday. Says the cap is fine.
Something still doesn't seem right to me. He insists the used cap he leaves in the unit is fine (even though it needs to be bumped to start the fan - not kidding)
Frustrated that I got what seems like two bad diagnosis/techs, I read up on hvac (I was a navy radar tech, never an HVAC tech) and refresh my memory on how to test fan motors and capacitors.
I ohm out the fan. Heres the readings:
Black to Purple: 29.1
Black to Brown: 66.7
Purple to Brown: 94.1
So, 1 to 2 ohm off.
My understanding (based on some youtube videos) is if Bk2Pu+Bk2Br=Pu2Br or very close, then the fan is good.
None of the 3 terminals show shorted to capacitor exterior btw.
Also, FAN spins freely when not energized. I feel, hear, see no signs of bad/degraded bearings. I think the reason the fan didn't work for the first tech was it was overheated and was in overtemp shutdown mode.
Capacitance Readings on the 5/45uF 440V dual capacitor.
Common to Fan:0 uF (instead of 5uF +/-5%)
Common to Herm: 28 uF (Instead of 45uF +/- 5%)
MY diagnosis: Bad capacitor (no doubt), fan is fine (?)
Two questions:
1) IS MY FAN BAD ALSO, BASED ON THE SYMPTOMS AND READINGS GIVEN?
2) I ordered a new cap off Amazon. Fan and Cap dont arrive till tuesday (its sunday). CAN I SAFELY RUN THE AC WITH A CAPACITOR THAT READS 0uF/28UF VS 5uF/45uF if I just bump start the fan, and let it to cool all day. ( Ill shut it off at night) Will this damage my unit in any way?
Thank you!