Bad Circuit Breaker????

1345 Views 3 Replies 4 Participants Last post by  Speedy Petey
Had power (volts/amps) to a circuit...receptacle, small wall heater and another receptacle (all 110vac). My grandson was pulling the plug out of the 1st receptacle....installed a "twist and snap closed" receptacle cover. He kept pulling the plug out but it snapped closed.

Lost power to all 3 (2 receptacles and heater). Same circuit where plug was being pulled out. Have replaced the 1st receptacle, all lug connections, no back wiring, still no power. Checked everything with voltage checker and wand...nothing. Checked all breakers (on/off test and tested with wand) not finding a bad breaker. Bought a Breaker Finder/Tester. Will that be reliable in finding a faulty breaker, if that's the case? Don't want to start pulling breakers out unless I'm fairly certain.

Any other thoughts or ideas?

Thanks,

Bob---PA
1 - 1 of 4 Posts
There is NO way you can accurately troubleshoot with a want tester alone.
You say you checked all the breakers and they did show power with the wand anyway. What makes you thin it is a bad breaker?

For you and anyone else reading this in the future. 99% of the time the breaker is either good, or is good and doing it's job if tripping. It's most likely NOT a bad breaker.