I am having my second story remodeled and wanted to take a stab at the wiring diagram to be able to have a good understanding of what will take place and to be up to speed when the contractor lays out the plan.
Notes on circuits:
All (non-bathroom) receptacle outlets will be 20Amp AFCI breakers/#12 Romex
All (non-bathroom) lighting/fan fixture will be 15Amp/#12 Romex
Bathroom Vent/Heater will be dedicated 20Amp breaker/#12 Romex
Bathroom receptacles/lighting fixtures will be dedicated (first receptacle is GFCI) - 20Amp/#12 Romex
I live in Dallas, TX.
From my understanding, lighting/fan circuits could've been #14 Romex/15 Amp breakers
All lighting will be CFLs (understand the load per circuit is lower than needed - just trying to understand laying out the circuits)
The master bedroom has a circuit heading to the attic for a few light fixtures.
Apologies for any pertinent information left out and for the non-professional look/feel to the diagram.
Any/all comments will truly be appreciated.
Thank you,
Marc
Notes on circuits:
All (non-bathroom) receptacle outlets will be 20Amp AFCI breakers/#12 Romex
All (non-bathroom) lighting/fan fixture will be 15Amp/#12 Romex
Bathroom Vent/Heater will be dedicated 20Amp breaker/#12 Romex
Bathroom receptacles/lighting fixtures will be dedicated (first receptacle is GFCI) - 20Amp/#12 Romex
I live in Dallas, TX.
From my understanding, lighting/fan circuits could've been #14 Romex/15 Amp breakers
All lighting will be CFLs (understand the load per circuit is lower than needed - just trying to understand laying out the circuits)
The master bedroom has a circuit heading to the attic for a few light fixtures.
Apologies for any pertinent information left out and for the non-professional look/feel to the diagram.
Any/all comments will truly be appreciated.
Thank you,
Marc