Found your problem! You have PVC conduit connecting the panels. If you had used EMT metal conduit, that would've taken care of ground path for you.
But hold on. I have an idea.
Whenever I install two
panels next to each other, I always stick 2-3 "convenience pass-throughs" e.g. of 3/4" conduit. You never know when those will be useful e.g. for rerouting a circuit to the other panel... but they are so nice to have when you need one! At least one "near the top" and one "near the bottom". So I would go look to see if you have knockouts that mostly line up, and if so, straight shot. If not, it might take some fidgeting with offset nipples.
Cheap, and kills 2 birds with one stone.
Also, while the panel is off... you know your needs but I encourage people to be extreme in buying extra panel spaces. We see too many people go "I'm out of spaces, help" and that's
so easily avoided at panel-buy time (i.e. now). So while it's off, I would take it back and get a 30-space, the difference in price is ... a pizza.
Those GE breakers count as half a space. You can't count on double-stuffing spaces anymore, because new and remodel circuits usually require AFCI or GFCI, and that's usually best (or only) done at the breaker.
Still, your panel needs a ground bar. It doesn't have one (that is ALL neutral bar) and you need to put grounds in legal places instead of where they are.
Thank you ServiceCall, I don't see anymore predrilled spots for a new bar unless I can rough the paint and add a new one using self tapping screws? Would you jumper between the neutral and new ground bar or just ground to the box alone?
Your panel is all neutral bars and doesn't have any ground bars at all (unless it's hiding under that mop of neutrals or something).
But surely GE left you a site for a ground bar (possibly hiding). I strongly encourage you to populate it, and move all your grounds to it. See if the label calls out a particular ground bar model and see if GE still offers it.
However, yes, if you need to make your own ground bar site with self-tapping screws, that is fine.
If the screw thread pitch is -32 or finer, that will suffice as an electrical connection. Otherwise, wire one with some of that grounding electrode wire you no longer need.
Half-FastEddie, thank you for pointing that out. I overlooked that before, NEC says 3 ground under same term as far as I can find. I will relocate one of those! Thanks!
No. When they say "3 ground under a lug" they're referring to
the small lugs e.g. those on the neutral bar and most of the ones on the ground bar. They do not mean spooge a bunch of wires on the large-wire lug. I see it all the time but it doesn't work. Since grounds are only used when there's a faulting appliance, that little monster can hide until you need it to work.