210.52 basically covers all typical receptacles in a home, so yes, if you have a basement with power TR is required unless it is behind a large appliance.
210.52 basically covers all typical receptacles in a home, so yes, if you have a basement with power TR is required unless it is behind a large appliance.406.12 Tamper-Resistant Receptacles for Dwelling Units
In all areas specified in 210.52, all nonlocking-type 125-volt, 15- and 20-ampere receptacles shall be listed tamper-resistant receptacles.
Exception: Receptacles in the fol lowing locations shall not be required to be tamper-resistant:
1) Receptacles located more than 1.7 m (5½ ft) above the floor.
2) Receptacles that are part of a luminaire or appliance.
3) A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected in accordance with 400.7(A)(6), (A)(7), or (A)(8).
4) Nongrounding receptacles used for replacements as permitted in 406.4(D)(2)(a).