No, you have to check for power where the humidifier is tapped off of, either a transformer in the heating unit or terminals on the control board.
 

· Registered
Joined
·
5,919 Posts
try to get a picture of set up and control board...from what you say the transformer from humidifier is connected to control board...this is correct..now you need to see if you have 110 volt at control board terminals powering up the trans...then you need to see if you have 24 volts leaving the trans...
 

· Registered
Joined
·
6 Posts
Discussion Starter · #7 ·
try to get a picture of set up and control board...from what you say the transformer from humidifier is connected to control board...this is correct..now you need to see if you have 110 volt at control board terminals powering up the trans...then you need to see if you have 24 volts leaving the trans...
How do you post picture? Above the HUM connection. I checked voltage and it was 120 volts. Nothing before or after the transformer.
 

· Registered
Joined
·
17,804 Posts
check the voltage output of secondary side of the humidifier transformer.

120 v in and no or low voltage out indicates that the transformer is bad, otherwise you have to check the wires feeding the humidifier and humidistat.
 

· In Loving Memory
Joined
·
42,671 Posts
The HUM terminal is only energized when the furnace has a heat call. Did you check for voltage with the thermostat calling for heat, and the safety switch closed.
 

· In Loving Memory
Joined
·
42,671 Posts
The wire on the W terminal. When the furnace is getting a heat call(with the safety switch closed/pressed) you should get 24 volts from W to C/common.
 