No power before or after the transformer.No, you have to check for power where the humidifier is tapped off of, either a transformer in the heating unit or terminals on the control board.
It says Armstrong Air. Board says Honeywell Smartvalve 11.post furnace model and brand.
what's the transformer connected to?
How do you post picture? Above the HUM connection. I checked voltage and it was 120 volts. Nothing before or after the transformer.try to get a picture of set up and control board...from what you say the transformer from humidifier is connected to control board...this is correct..now you need to see if you have 110 volt at control board terminals powering up the trans...then you need to see if you have 24 volts leaving the trans...
What wire would it be for the thermostat calling for heat? I have 5wires hooked to the board and the white is the only one not getting 24vThe HUM terminal is only energized when the furnace has a heat call. Did you check for voltage with the thermostat calling for heat, and the safety switch closed.