I am going to add a sub panel to an unfinished area of my basement for the relocation of my airconditoners and future expansion. The existing primary panel is located in a finished area of the basement so it is difficult to route circuits to.
A few data points; Cook County, IL so mandatory EMT, 200A main panel circa 1995.
I have a 3/4” abandoned EMT conduit run (60’ long) from the main panel to the unfinished area which saves me a lot of work trying to route a conduit run in a finished area. I’d like to maximize the amperage of the feeder to the sub panel. Based on conduit fill I see I am limited to two #4 or four #6 wires in the conduit. Since I am using EMT, the pipe will be ground so I need three wires in the conduit. Each phase plus neutral. I see if I run three #6 THHN I can run 75 A current at 90 degrees. I plan a lug style sub panel without a main breaker. 12 or 16 circuits. Bonding screw will be removed.
So my questions are:
1) ok to use 90 degree rating for THHN for a feeder ( in EMT) to a sub panel?
2) Can I round up the 75A rating for the THHN wire to 80A for the breaker at the main panel feeding the sub or do I round down to 70A? I know 70A 2P breakers are available but not sure 80A is very common.
3) if I had another conduit run to the unfinished area could I up the gauge to #4 and run two #4 wires in the 3/4” and the third #4 in another conduit run? Or does the feeder set have to be in the same raceway? Not sure I want to do this anyway but wondering if the feeder set must be intact the entire run.
Any other ideas how I maximize the current to the sub panel based on my unusual constraints. Running 1 1/4” EMT would be very difficult due to finished drywall ceilings....
Sent from my iPad using Tapatalk
A few data points; Cook County, IL so mandatory EMT, 200A main panel circa 1995.
I have a 3/4” abandoned EMT conduit run (60’ long) from the main panel to the unfinished area which saves me a lot of work trying to route a conduit run in a finished area. I’d like to maximize the amperage of the feeder to the sub panel. Based on conduit fill I see I am limited to two #4 or four #6 wires in the conduit. Since I am using EMT, the pipe will be ground so I need three wires in the conduit. Each phase plus neutral. I see if I run three #6 THHN I can run 75 A current at 90 degrees. I plan a lug style sub panel without a main breaker. 12 or 16 circuits. Bonding screw will be removed.
So my questions are:
1) ok to use 90 degree rating for THHN for a feeder ( in EMT) to a sub panel?
2) Can I round up the 75A rating for the THHN wire to 80A for the breaker at the main panel feeding the sub or do I round down to 70A? I know 70A 2P breakers are available but not sure 80A is very common.
3) if I had another conduit run to the unfinished area could I up the gauge to #4 and run two #4 wires in the 3/4” and the third #4 in another conduit run? Or does the feeder set have to be in the same raceway? Not sure I want to do this anyway but wondering if the feeder set must be intact the entire run.
Any other ideas how I maximize the current to the sub panel based on my unusual constraints. Running 1 1/4” EMT would be very difficult due to finished drywall ceilings....