The quotes from this company range between 6-9K. I was told $1500 for labor, $1200 for parts, the rest for equipment. Seem high?
Sorry I'm such a newbie, but what might this require for the size I'm doing, 2.5T? 240 or 120? Amperage?Your current A/C circuit should suffice for a heat pump, but he may have meant you need another circuit for the heat strips. If your breaker box is not big enough, it will have to be upgraded.
Heat Strips start at 5KW and get bigger and are all 240V. You will likely need more than one depending on how much heat you need. So adding the heat strips together, the total KW you can figure the amps and size the circuit accordingly.Sorry I'm such a newbie, but what might this require for the size I'm doing, 2.5T? 240 or 120? Amperage?
So that's 5000w/240v = 21 amps. What amp breaker would that be?Heat Strips start at 5KW and get bigger and are all 240V. You will likely need more than one depending on how much heat you need. So adding the heat strips together, the total KW you can figure the amps and size the circuit accordingly.
The AC couldn't maintain 80 on an 85 degree or hotter day, but it did have a slow leak. It basically ran ...until the blower motor (and cap?) cooked itself today... 16-18 hours a day at that temp or higher. Basically it was only off between 1am and 8am. Its not going to kill me being out, but it sucks for now. It's been 95+ for nearly a week.Regarding undersized, has your present unit been running at full capacity? My oversized gas furnace runs 1/4th of the time during an average, or slightly colder, winter.
1362 HDD for January for Dayton, OH. At 8 cents/kwh average rate in Ohio this is 8.7 kw all the time, 7 therms in 24 hrs.getting a $500+ electric bill in January was not expected.
It was borderline based on the numbers I ran, but since I couldnt find 125 amp breakers for my #2 copper cable, I used 100 amp.A 100 amp sub panel is undersized for a 20 KW strip heat package and any other load.
Dayton Power and light charges 10.5 cents per KW/Hr.1362 HDD for January for Dayton, OH. At 8 cents/kwh average rate in Ohio this is 8.7 kw all the time, 7 therms in 24 hrs.
For a 2000 sq. ft. house including basement it's 350 BTU/day/sq.ft.
1362 HDD/31 days = 43.9 HDD in one day
350/43.9 = 7.8 BTU/sq.ft./HDD, slightly above the average 6 BTU/sq.ft./HDD.
For a $500 elec. bill @10.5 cents/kwh you must have used 4762 kwh during this 31 day period, or 154 kwh per 24 hr day.Dayton Power and light charges 10.5 cents per KW/Hr.
As for the rest of your post, I am not sure I understand it.