Sorry for the improper nomenclature, but this is my problem.

I am replacing my evaporator coil that is connecting to my air handler.
Old coil dimensions are 33.5 x 25 x 12 and all the newer 4 ton evaporator coils are 39 x 25 x 12. The 39 inches wide will not fit in the current layout in the attic. Can I order some sort of angled piece that transitions from my furnace to coil at an angle in order for it to fit?

Thanks for the help!
 

·
Registered
Joined
·
1,407 Posts
You can use flexboard to deal with this space. The most important is replacing the TXV to match condenser .
 

·
Registered
Joined
·
51 Posts
Discussion Starter #3
You can use flexboard to deal with this space. The most important is replacing the TXV to match condenser .
Hey thanks!
How do I know if I currently have a TXV installed and is it required to have one in the new replacement?
 

·
Registered
Joined
·
1,407 Posts
You have to install a new TXV even it comes with a new coil. The new TXV has to match the condenser specs.
 

·
Registered
Joined
·
51 Posts
Discussion Starter #5
You have to install a new TXV even it comes with a new coil. The new TXV has to match the condenser specs.
I am getting a 4 ton coil to match my 4 ton condenser.
Even though they are the same tonnage they might not be comparable?
What else do I need to look at?
 

·
Registered
Joined
·
1,407 Posts
if the coil replacement has the same tonnage and seer that's ok. Ask the store guy
 