Article 430.102 of the code (motors) states that the disconnecting means shall be in sight of the motor.
Article 100 (definitions) states that 'in sight' means visible and not more than 50'.
I'd say you're good.
The only issue would be that the code states that the disconnecting means needs to be capable of being locked in the open position but I've yet to see that enforced.
Article 100 (definitions) states that 'in sight' means visible and not more than 50'.
I'd say you're good.
The only issue would be that the code states that the disconnecting means needs to be capable of being locked in the open position but I've yet to see that enforced.