Getting ready to run a 30 amp dedicated circuit in my garage for a new air compressor and have a question regarding a disconnect switch. I've read that a disconnect is required within 6 feet of the compressor but, since my compressor will be installed 5 feet from the breaker panel is it required? The panel is next to the service door and I plan on running 10/2 romex to a junction on the other side of the door, then hardwiring a cable from the junction box to the compressor.
 

· Registered
Joined
·
216 Posts
Discussion Starter · #3 ·
A breaker within sight of the compressor can be considered a disconnect.
So can a cord and plug if the compressor has one.
Thanks Joe,
Compressor is a Puma 60 gallon with a 5HP motor and the book says is should be hardwired so I am going to use a 6' cable hardwired to the junction so I can move it away from the corner if and when it needs servicing. Here's a pic of where it will be going. Breaker and compressor will be within an arms reach of each another.
 

Attachments

· Idiot Emeritus
Joined
·
1,910 Posts
Article 430.102 of the code (motors) states that the disconnecting means shall be in sight of the motor.

Article 100 (definitions) states that 'in sight' means visible and not more than 50'.

I'd say you're good.

The only issue would be that the code states that the disconnecting means needs to be capable of being locked in the open position but I've yet to see that enforced.
 